Maximum number of wireless devices per Panel Server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Maximum number of wireless devices per Panel Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Anton_Balanescu
Ensign Anton_Balanescu
Ensign

Posted: ‎2022-05-05 04:46 PM . Last Modified: ‎2022-05-12 07:52 AM

1 Like
3
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-05 04:46 PM

Maximum number of wireless devices per Panel Server

Hello team, 

 

Could you tell me please how many wireless devices can I connect to one Panel Server?

 

Thanks!

Anton

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Labels
  • Labels:
  • Product selection
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2022-05-05 11:25 PM

1 Like
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-05 11:25 PM

Hi @Anton_Balanescu ,

If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:​

- 20 PowerTag/PowerLogic Tag or Acti9 Active ​

- 3 PowerLogic HeatTag​

- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.

 

Please refer to Panel Server Firmware Release Notes for more details.

 

BR​

See Answer In Context

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Tags (1)
  • Tags:
  • english
Reply
Replies 3
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2022-05-05 11:25 PM

1 Like
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-05 11:25 PM

Hi @Anton_Balanescu ,

If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:​

- 20 PowerTag/PowerLogic Tag or Acti9 Active ​

- 3 PowerLogic HeatTag​

- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.

 

Please refer to Panel Server Firmware Release Notes for more details.

 

BR​

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Tags (1)
  • Tags:
  • english
Reply
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2024-07-24 10:37 PM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 10:37 PM

Hi Szymon,

 

Is there an update on the max numbers for the latest firmware 001.010.000 from the previous response?

 

Also, can one powertag Acti9 be paired to 2 different panel servers (out of curiosity)?

 

Thanks.

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-07-25 07:45 AM

0 Likes
0
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-25 07:45 AM

Hello @jedzruiz1985 , 

Please keep the Panel Server Release Notes in your favorites:

https://www.productinfo.schneider-electric.com/ecostruxurepanelserverrn/doca0178-ecostruxure-panel-s...

 

Max wireless configuration is well described for each ref of Panel Server.

 

To your question : "Also, can one powertag Acti9 be paired to 2 different panel servers (out of curiosity)?"

Answer is "no". Communication between PowerTag sensor and Panel Server is encrypted with a specific key. You can only pair a PowerTag Sensor with ONE Panel Server at a time.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore