Hello team,
Could you tell me please how many wireless devices can I connect to one Panel Server?
Thanks!
Anton
- Labels:
-
Product selection
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Anton_Balanescu ,
If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:
- 20 PowerTag/PowerLogic Tag or Acti9 Active
- 3 PowerLogic HeatTag
- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.
Please refer to Panel Server Firmware Release Notes for more details.
BR
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Anton_Balanescu ,
If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:
- 20 PowerTag/PowerLogic Tag or Acti9 Active
- 3 PowerLogic HeatTag
- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.
Please refer to Panel Server Firmware Release Notes for more details.
BR
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Szymon,
Is there an update on the max numbers for the latest firmware 001.010.000 from the previous response?
Also, can one powertag Acti9 be paired to 2 different panel servers (out of curiosity)?
Thanks.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985 ,
Please keep the Panel Server Release Notes in your favorites:
Max wireless configuration is well described for each ref of Panel Server.
To your question : "Also, can one powertag Acti9 be paired to 2 different panel servers (out of curiosity)?"
Answer is "no". Communication between PowerTag sensor and Panel Server is encrypted with a specific key. You can only pair a PowerTag Sensor with ONE Panel Server at a time.
Regards,
Solution Architect - France Operations