Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82561members
350171posts

Maximum number of wireless devices per Panel Server

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

Solved
Anton_Balanescu
Ensign
Ensign
0 Likes
1
357

Maximum number of wireless devices per Panel Server

Hello team, 

 

Could you tell me please how many wireless devices can I connect to one Panel Server?

 

Thanks!

Anton

Tags (1)

Accepted Solutions
Szymon_Hochół
Commander Commander
Commander
0 Likes
0
350

Re: Maximum number of wireless devices per Panel Server

Hi @Anton_Balanescu ,

If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:

- 20 PowerTag/PowerLogic Tag or Acti9 Active 

- 3 PowerLogic HeatTag

- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.

 

Please refer to Panel Server Firmware Release Notes for more details.

 

BR​

See Answer In Context

Tags (1)
1 Reply 1
Szymon_Hochół
Commander Commander
Commander
0 Likes
0
351

Re: Maximum number of wireless devices per Panel Server

Hi @Anton_Balanescu ,

If you connect ONLY Easergy TH100/CL110 sensors you can have up to 65 of them under one gateway. But if you combine different types of supported wireless devices under one gateway you can have up to 30 of them, with a maximum of:

- 20 PowerTag/PowerLogic Tag or Acti9 Active 

- 3 PowerLogic HeatTag

- 6 wireless indication auxiliaries for ComPacT and PowerPacT circuit breakers.

 

Please refer to Panel Server Firmware Release Notes for more details.

 

BR​

Tags (1)