Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hello,
by using a ion meter with internal storage the historical data is first stored on the device and always visible in case there is a communication problem to the pme server.
Is the same possible by using a Com'X510 with active data logging and several non ION slaves?
thank you
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
Yes, it is possible as described in the following document from PC based logging in PME with ETL log insertion from EGX/ComX discussion.
Best regards,
Bojan
Link copied. Please paste this link to share this article on your social media post.
Hello Bojan,
but with etl I lose the real time values in pme. With an Ion Meter I do have both!
Or am I wrong?
Link copied. Please paste this link to share this article on your social media post.
Hi Sven,
The idea is to add a meter in PME as usual, and then use ETL for backfilling in order to achieve the internal storage of the historical data functionality in case there is a communication problem to the server.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.