Ecostruxure Panel Server PAS600L Observations - Digital Inputs
Please provide assistance with dot point 1a, and correct any incorrect observations below about PAS600L Digital Inputs:
:
1. with Firmware 001.001.001 and 001.002.000:
a. DI can only be used as a counter, it would seem. When DI is configured for Standard Input (or 'Status') in EPC software, Modbus registers 41003 and 41004 are not set to'1' as indicated in user manual. Additionally, DI status value is not measurable in registers 41053 and 41054 when DI is configured as Standard Input (register value seems to stay as -1 whether or not 24V DI contact is open/closed)
b. Could not determine what float32 registers 41173 and 41175 express as they change with each pulse.
2. with Firmware 001.002.000:
a. DI input configuration set up with firmware 1.1.1 was overwritten during the firmware upgrade. (It showed in Ecostruxure Power Commission as 'unwired' following the upgrade).
b. The new 'measurement' tab in PAS600L webpages does not allow Digital Inputs that are configured to be selected (Refer screenshot)
3. with Firmware 1.1.1
a. The latest Firmware upgrade file in the format required for installation using the web server was not located.