Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
EM4200 and iem3000 On a Daisy-Chain with Link 150
Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2017-07-1707:27 AM
EM4200 and iem3000 On a Daisy-Chain with Link 150
TEAM:
We have one EM4200 and twelve iem3000 On a Daisy-Chain with a Link 150. The serial port was set to 9600, None, Stop Bit Automatic. The iem3000 units came in fine but the EM4200 (new Enercept) would not communicate.
The fix is to change the stop bit from Automatic to 1. The iem meters were happy and the EM4200 started working. Even with the stop bit at Automatic Vista did not complain but it also did not return any live data.
NOTE: The latest rev I could find for ION Setup has an EM4200 device type but does not have live data tables for this meter. Had to create a unit in PME for testing.