EM4200 and iem3000 On a Daisy-Chain with Link 150
TEAM:
We have one EM4200 and twelve iem3000 On a Daisy-Chain with a Link 150. The serial port was set to 9600, None, Stop Bit Automatic. The iem3000 units came in fine but the EM4200 (new Enercept) would not communicate.
The fix is to change the stop bit from Automatic to 1. The iem meters were happy and the EM4200 started working. Even with the stop bit at Automatic Vista did not complain but it also did not return any live data.
NOTE: The latest rev I could find for ION Setup has an EM4200 device type but does not have live data tables for this meter. Had to create a unit in PME for testing.