EIFEs are connected to PME but the data is not logged in the database

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EIFEs are connected to PME but the data is not logged in the database
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Monitoring Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
JimmyFSA
Crewman JimmyFSA
Crewman

Posted: ‎2023-09-19 12:25 PM

0 Likes
4
1219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-19 12:25 PM

EIFEs are connected to PME but the data is not logged in the database

Hello everyone,

We have connected several EIFEs in daisychain on a TCP network. All the EIFEs are configured in a similar way and we can ping each of them from the application server.
We have a tool (PMCModbus) that lets us know which modbus elements are connected behind an IP gateway. Here too, everything seems to be communicating perfectly on Port 502.
Since Vista, real-time data is not available and historical values are not logged in the database. Only on one gateway in the chain is the data available and logged.
Do you have any idea why data from only one gateway is logged?
Thank you for your help.
Jimmy

  • Thumbnail of EcoStruxure™ Power Monitoring Expert
    Schneider Electric
    EcoStruxure™ Power Monitoring Expert
View products (1)
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • eife
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-09-20 12:08 AM

0 Likes
2
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-20 12:08 AM

Hello @JimmyFSA , 

Better check this topic with the tech support. Please include a PME Diagnostic file (this will include devices communication status).

 

Many questions for you:

  1. What is your version of PME ?
  2. What is the Firmware of your EIFEs ? 
  3. What is the position of the working IFE in the chain ?
  4. Can you see all your MTZ with EPC installed on the PME server ?
  5. What is the cradle position of your MTZ ?
  6. Did you check the devices status with the PME Diagnostic Viewer ?
    • Below example of a MTZ communicating correctly with PME
    • Romain_Polette_0-1695193302334.png

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
JimmyFSA
Crewman JimmyFSA
Crewman

Posted: ‎2023-10-05 01:11 AM

0 Likes
1
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-05 01:11 AM

Hello @Romain_Polette ,

 

You will find my answers below

  1. What is your version of PME ? 2022
  2. What is the Firmware of your EIFEs ? I've added a screenshot to the attachment
  3. What is the position of the working IFE in the chain ? the second one I've added a screenshot to the attachment
  4. Can you see all your MTZ with EPC installed on the PME server ? Yes, we have one that is in IFE Boot that we need to update and we have two spare bases equipped with EIFE.
  5. What is the cradle position of your MTZ ? inserted
  6.  Did you check the devices status with the PME Diagnostic Viewer ? Yes I've added a screenshot to the attachment
Attachments
Reply
JimmyFSA
Crewman JimmyFSA
Crewman

Posted: ‎2023-10-05 01:12 AM

0 Likes
0
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-05 01:12 AM

Please find the diagnostic file

Attachments
Diagnostique.zip
Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-10-05 04:49 AM . Last Modified: ‎2023-10-05 04:50 AM

0 Likes
0
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-05 04:49 AM

Hello @JimmyFSA , 

 

The diagnostic file must be investigated through a tech support ticket:

https://www.se.com/ch/fr/work/support/customer-care/contact-schneider-electric.jsp

 

It seems that PME can only read Serial Number and FW version for 30Q1 and 20Q0 MTZ.

Tech support should discover why only 2 breakers are communicating with PME, especially if you can ping all the chain and communicate through Modbus TCP.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of