EIFEs are connected to PME but the data is not logged in the database
Hello everyone,
We have connected several EIFEs in daisychain on a TCP network. All the EIFEs are configured in a similar way and we can ping each of them from the application server.
We have a tool (PMCModbus) that lets us know which modbus elements are connected behind an IP gateway. Here too, everything seems to be communicating perfectly on Port 502.
Since Vista, real-time data is not available and historical values are not logged in the database. Only on one gateway in the chain is the data available and logged.
Do you have any idea why data from only one gateway is logged?
Thank you for your help.
Jimmy
- Labels:
-
troubleshooting
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @JimmyFSA ,
Better check this topic with the tech support. Please include a PME Diagnostic file (this will include devices communication status).
Many questions for you:
- What is your version of PME ?
- What is the Firmware of your EIFEs ?
- What is the position of the working IFE in the chain ?
- Can you see all your MTZ with EPC installed on the PME server ?
- What is the cradle position of your MTZ ?
- Did you check the devices status with the PME Diagnostic Viewer ?
- Below example of a MTZ communicating correctly with PME
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette ,
You will find my answers below
- What is your version of PME ? 2022
- What is the Firmware of your EIFEs ? I've added a screenshot to the attachment
- What is the position of the working IFE in the chain ? the second one I've added a screenshot to the attachment
- Can you see all your MTZ with EPC installed on the PME server ? Yes, we have one that is in IFE Boot that we need to update and we have two spare bases equipped with EIFE.
- What is the cradle position of your MTZ ? inserted
- Did you check the devices status with the PME Diagnostic Viewer ? Yes I've added a screenshot to the attachment
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @JimmyFSA ,
The diagnostic file must be investigated through a tech support ticket:
https://www.se.com/ch/fr/work/support/customer-care/contact-schneider-electric.jsp
It seems that PME can only read Serial Number and FW version for 30Q1 and 20Q0 MTZ.
Tech support should discover why only 2 breakers are communicating with PME, especially if you can ping all the chain and communicate through Modbus TCP.
Regards,
Solution Architect - France Operations