Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi,
I was going through the user guide for the EGX300 and came across the following section.
Which Schneider devices are using the powerlogic protocol? Will this cover all of the Schneider power products such as NSX/NW and Power meters? If it is only referring to specific devices, is there a list of these?
Thanks for your assistance with this.
Thanks,
Martin
Link copied. Please paste this link to share this article on your social media post.
Which Schneider devices are using the powerlogic protocol?
Basically those are SquareD legacy devices.
Devices that use PowerLogic protocol (Sy-Max):
Series 100, 200, 2000 Circuit Monitors (CM100, CM200, CM2000)
Series 600 Power Meters (PM600)
Digital Relays (DR1000 = "Americanized" SEPAM1000)
PowerLogic PIF-3 - product interface to the Micrologic Series 2 Circuit Breakers
PowerLogic PIF-85 - product interface to the Lifeguard Model 85 Transformer Temperature Controller.
PowerLogic Gateways: EGX100, EGX300, PM8ECC
PowerLogic legacy Gateways: EGX200 and EGX400.
Will this cover all of the Schneider power products such as NSX/NW and Power meters?
No, this will not cover all Schneider power products. Today, Compact NSX, Masterpact NW and Power Meters talk Modbus RTU.
Link copied. Please paste this link to share this article on your social media post.
Which Schneider devices are using the powerlogic protocol?
Basically those are SquareD legacy devices.
Devices that use PowerLogic protocol (Sy-Max):
Series 100, 200, 2000 Circuit Monitors (CM100, CM200, CM2000)
Series 600 Power Meters (PM600)
Digital Relays (DR1000 = "Americanized" SEPAM1000)
PowerLogic PIF-3 - product interface to the Micrologic Series 2 Circuit Breakers
PowerLogic PIF-85 - product interface to the Lifeguard Model 85 Transformer Temperature Controller.
PowerLogic Gateways: EGX100, EGX300, PM8ECC
PowerLogic legacy Gateways: EGX200 and EGX400.
Will this cover all of the Schneider power products such as NSX/NW and Power meters?
No, this will not cover all Schneider power products. Today, Compact NSX, Masterpact NW and Power Meters talk Modbus RTU.
Link copied. Please paste this link to share this article on your social media post.
Awesome. Thank you
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.