Com'X 200 logged data

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X 200 logged data
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-04-23 01:44 AM

1 Like
10
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 01:44 AM

Com'X 200 logged data

Hi there,

We have an installation with 3 Conext TL grid-tie inverters that are connected over Modbus RTU to a Com'X 200 and a 4-20mA solar sensor which is directly connected to the Com'X. The Com'X has Firmware V1.0.14.

For the Conext TL we had to create a custom device type. The data is logged every 15 minutes and send once per hour to EO.

No we found the following strange behaviour:

In the XLM file which is send to EO we have different timestamps for all of the devices. Eg two Conext have logged data from 06:00 until 06:45 and the third one and the solar sensor from 06:15 until 07:15

Has someone else noticed a similar problem?

Thanks

Daniel

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-07-21 09:44 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-21 09:44 AM

Daniel

This is due to the fact that the 2 processes ("data acquisition" and "data publication") are totally independant :

Example : let us imagine that we configure data acquisition with 15 minutes period, and data acquisiton with 1 hour period,

At 12:00, the first process ("data acquisition") is waked up and starts to collect data from the different slaves,

At the same time, the second process ("data publication") is also waked up and start to connect to the data publication site (eg a FTP server).

using "login", "password", "type", ... commands

Depending on the responce time of modbus slaves compared to the connection time of the FTP server,

We can understand that some time, the data publication process will send the logged data before than the last data in the last slave have been collected.

Nothing is lost in the data log, but the "late" data will be publlished at the next occurence of the data publication

Regards

See Answer In Context

Reply
Replies 10
Anonymous user
Not applicable

Posted: ‎2014-04-23 05:16 AM

0 Likes
3
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 05:16 AM

Hello Daniel

What is the destination platform (where data are published)

Could it be possible to have a copy of the backup file

Regards

Jef

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-04-23 05:22 AM

0 Likes
2
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 05:22 AM

Hi Jef,

The destination platform is Energy Operation. Unfortunately I don't have a backup file and nobody is on site. But I can see with my colleague who has programmed the Com'X.

The only thing I can provide you for the moment is a copy of the XML file which is sent to the Energy Operation server.

Regards

Daniel

Reply
Anonymous user
Not applicable

Posted: ‎2014-04-23 05:26 AM

0 Likes
1
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 05:26 AM

if it was possible to get the xml file, it should help

Regards

Jef

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-04-23 05:30 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-23 05:30 AM

OK, I will send it by email

Reply
Anonymous user
Not applicable

Posted: ‎2014-07-21 09:44 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-21 09:44 AM

Daniel

This is due to the fact that the 2 processes ("data acquisition" and "data publication") are totally independant :

Example : let us imagine that we configure data acquisition with 15 minutes period, and data acquisiton with 1 hour period,

At 12:00, the first process ("data acquisition") is waked up and starts to collect data from the different slaves,

At the same time, the second process ("data publication") is also waked up and start to connect to the data publication site (eg a FTP server).

using "login", "password", "type", ... commands

Depending on the responce time of modbus slaves compared to the connection time of the FTP server,

We can understand that some time, the data publication process will send the logged data before than the last data in the last slave have been collected.

Nothing is lost in the data log, but the "late" data will be publlished at the next occurence of the data publication

Regards

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2014-09-08 05:05 AM

0 Likes
4
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-08 05:05 AM

Daniel,

This might be a bit of topic, but we are trying to integrate the Context TL inverters into a PME 7.2.2 installation and we can't find drivers. I'm just wondering if you would be willing to share the Modbus Driver for the Com'X 200 which might give us a head start?

Thanks.

James

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-09-08 05:29 AM

0 Likes
2
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-08 05:29 AM


Hi James,

Unfortunately we don't have any remote access to this site, what means, that someone has to go on site to get the driver. But I don't think, that it would help you a lot, as we are only reading the real energy of the Conext and that's it.

If you need the Modbus Register list, I can provide it to you.

Sorry

Daniel

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2014-09-08 05:40 AM

0 Likes
1
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-08 05:40 AM

Daniel,

Thanks. It was worth asking. 🙂

Yes, if you could just provide me the register list, we could whip something up.

Cheers!

James

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-09-08 05:50 AM

1 Like
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-08 05:50 AM

OK, here we go!

You know: It's always worth for asking !

Daniel

Attachments
Reply
Anonymous user
Not applicable

Posted: ‎2014-09-08 06:27 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-09-08 06:27 AM

Hello James

Daniel mentionned the version was 1.0.14.

In this version there are no custom model (they have been added since version 1.1.x)

without the custom model, it will be difficult to "export" a device mapping model.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of