Do we have any software to install on a PC to emulate a serial modbus port ?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Do we have any software to install on a PC to emulate a serial modbus port ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-02-10 04:37 AM

0 Likes
9
2452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-10 04:37 AM

Do we have any software to install on a PC to emulate a serial modbus port ?

Hello,

I have a device connected to a link150 using RS485. I would like to emulate a Com port on my laptop to connect to the device.

The tool needs to allow me to enter IP address and slave device ID.

Do you have a handy tool ?

Thanking in advance,

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2022-02-10 05:09 AM

0 Likes
4
2450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-10 05:09 AM

We like to use Modsim 32 - https://www.win-tech.com/html/modsim32.htm

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-02-10 07:27 AM

0 Likes
3
2446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-10 07:27 AM

Thanks a lot Randi, but is it possible to use modsim to act as a virtual com port ?

I would like to use easergypro on my laptop to connect to serial port of protection relay through a link150.

Easergy pro does not allow to enter the slave ID of the relay....

Tags (1)
  • Tags:
  • english
Reply
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2022-02-15 01:48 AM

0 Likes
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 01:48 AM

Hi @Guillaume_Evrard 

I'm not aware of any software solution to be used with Link150, but I think that MOXA's NPort device could be what you are looking for. 

 

1.JPG

Tags (1)
  • Tags:
  • english
Reply
Olivier_GARAULT
Lieutenant JG Olivier_GARAULT Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-15 04:11 AM

0 Likes
3
2439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 04:11 AM

Bonjour, 

 

cela fait des années que l'on utilise Modscan32 et on n'a encore rien trouvé de mieux ni d'aussi simple et rapide.

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-02-15 05:07 AM

0 Likes
2
2437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 05:07 AM

Bonjour,

Comment fais-tu pour pouvoir avoir modscan32 = Com port Virtuel ?

 

Mon but est d'aller chercher un équipement connecté en série avec un logiciel qui ne permet pas d'entrer une adresse IP et un esclave modbus....

Tags (1)
  • Tags:
  • english
Reply
Olivier_GARAULT
Lieutenant JG Olivier_GARAULT Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-15 05:34 AM . Last Modified: ‎2022-02-15 05:42 AM

0 Likes
1
2435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 05:34 AM

Il faut configurer les IP sur la Link150 et dans modscan.

Configurer également la partie Modbus, par défaut on met 19200 8 bits 1 stop Even 0,5sec

sur la photo c'est un exemple pour lire une valeur sur un IM400. 

 

Au passage cela nous arrive de faire une formation à Rennes sur quelques basiques de la communication des équipements, pour des Schneider et des clients, cela dure une journée; (en support on utilise des TGBT Okken)

 

Capture d’écran 2022-02-15 142639.jpg

 

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-02-15 06:10 AM . Last Modified: ‎2022-10-19 01:06 AM

0 Likes
1
2427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 06:10 AM

Hello @sesa157458_brid , 

 

For use with eSetup Easergy Pro => I do not think this is possible.

Documentation is not mentioning this option:

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=eSetupEasergyPro_EN...


Not sure you can commission P3 or P5 through Link150. You can do some setup but only with the Web Pages of the device.

For P3 + eSetup EasergyPro => only through front face (COM port of your Laptop) or direct Ethernet.

 

Better ask here:

https://community.se.com/t5/PAE-Protection-Relays-Controllers/bd-p/energy-automation

 

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-02-15 07:04 AM

0 Likes
0
2424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 07:04 AM

Merci mais ce n'est pas mon besoin, et je connais modpoll, modscan....

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-02-15 07:06 AM

0 Likes
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-15 07:06 AM

In this case this a P1 and you can have Modbus S1 that seems modbus.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore