Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
107 | |
52 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Hi,
Why would a user not be able to access the setting for Pulse meter offset in a brand new Com'X 210 or Com'X510?
Logged into the COM'X 210 using Chrome, Firefox and Edge. Played with screen magnification. Didn't make a difference. Digital input (pulse) measurement properties advanced settings arrow toggles up and down but user can't enter the offset. (refer attachments. Offset not configurable when setting up the input either)
Configuring engineering units in the hardware is a requirement.
This has been seen before. What causes this? What is the solution?
Both Com'X210 and ComX510 have application version 6.5.4, MCU Board FW versiosn 2.2.6, Root Partition Version 4.2.2, Soft partition version 6.5.4, Hardware Version 5.
Link copied. Please paste this link to share this article on your social media post.
Hello @swil ,
This is a known issue with FW 6.5.4. You do not have access to the "Pulse Weight" AND "offset" parameters.
If you upgrade to 6.8.4 => this will fix the problem.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.