Display data in hexadecimal format on Panel Server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Display data in hexadecimal format on Panel Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-02-11 06:54 AM . Last Modified: ‎2025-02-11 06:55 AM

0 Likes
3
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 06:54 AM

Display data in hexadecimal format on Panel Server

Hi All,

 

I would like to inquire whether the panel server can display data in hexadecimal format?

 

I tried to integrate a field device into the Panel Server. I created a driver on EPC-W, and the data displayed on the panel server webpage shows 29014 (in decimal). However, this value is actually 7156 (from device’s HMI), which should be represented in hexadecimal format.

 

The following photos show my configuration, the data from the field device, and the test results from the Modscan. (Please disregard any differences in registers due to the offset.)

 

Stuart_Cheng_0-1739285589572.png

Stuart_Cheng_1-1739285598815.png

 

Stuart_Cheng_6-1739285679934.png

 

 

Stuart_Cheng_4-1739285617394.png

 

Stuart_Cheng_5-1739285625883.png

 

 

I'm not sure how to configure EPC-W to display the data in hexadecimal format. Does anyone has experience on this? Thank you!

 

 

 

 

 

 

 

 

 

Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-02-11 09:34 PM

1 Like
0
188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 09:34 PM

Hello @Stuart_Cheng,

There is no encoding to display the data in hexadecimal in PAS; you are able to check register in hexa using the modbus register diagnostic screen embeded in the PAS. INT16to INT16U would make sense.

I understand that the meter is providing data in hexa, but this is raw value what is the encoding used to get true measurement ? 7156 in hexa is 29014 in decimal/integer. If you get 36E7 what is the value in m3 ?

Kind regards

See Answer In Context

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-02-20 12:21 AM

0 Likes
0
130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 12:21 AM

Hello @Stuart_Cheng , 

It seems that EPC-W cannot managed packedBCD as an data input.

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-02-11 09:34 PM

1 Like
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 09:34 PM

Hello @Stuart_Cheng,

There is no encoding to display the data in hexadecimal in PAS; you are able to check register in hexa using the modbus register diagnostic screen embeded in the PAS. INT16to INT16U would make sense.

I understand that the meter is providing data in hexa, but this is raw value what is the encoding used to get true measurement ? 7156 in hexa is 29014 in decimal/integer. If you get 36E7 what is the value in m3 ?

Kind regards

Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2025-02-18 06:41 AM

0 Likes
0
145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-18 06:41 AM

Hi @Guillaume_Evrard,

 

Thank you for your response.
I obtained more detailed information from the vendor and discovered that the data type is actually PackBCD, not hexadecimal. Please refer to the image below.

Stuart_Cheng_0-1739889567339.png

 

This data is composed of registers 773 to 776, with each register divided into high and low words and represent values from 00 to 99. Finally, all the high and low words are combined into a single value.


For example, in the image:
(encoding from PackedBCD)
773: 0000 0000 , 0000 0000 ->     00
774: 0000 0000 , 0000 0011 -> 0003
775: 0111 0001 , 0101 0110 -> 7156
776: 0000 0000 , 0000 0100 ->     04

 

After combination would be 0000037156.04 -> 37156.04

 

Stuart_Cheng_1-1739889567445.png

 

 Wondering if our panel server can do this kind of encoding or calculation? Thank you

 

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-02-20 12:21 AM

0 Likes
0
131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 12:21 AM

Hello @Stuart_Cheng , 

It seems that EPC-W cannot managed packedBCD as an data input.

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of