Hi
In Panel Server document PLSED310196EN 2024 page 7 it is indicated = YES
In Panel Server release note DOCA0248EN-11 page 19, DOCA0178-15 page 12 it is indicated = Not Available
What is the status ?
Br/Anders
Link copied. Please paste this link to share this article on your social media post.
Hello Anders,
Panel Server is a DHCP client (ability to request/accept an IP address coming from a DHCP server) but not a DHCP server (ability to deliver a dynamic IP to DHCP clients)
Thanks to have raised the point (Doc team has been warned to correct catalogue).
Regards
Link copied. Please paste this link to share this article on your social media post.