DHCP Connection Fails for ComX510

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • DHCP Connection Fails for ComX510
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
107
Guillaume_Evrard
Captain Guillaume_Evrard Captain
52
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
swil
Commander swil
Commander

Posted: ‎2019-08-27 01:38 PM

0 Likes
4
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-27 01:38 PM

DHCP Connection Fails for ComX510

Can't connect to a ComX510 over Ethernet that has had a factory reset. With IPV4 settings for Ethernet to obtain an address automatically, can't get a response response from the ComX510 that displays a green light. Ethernet cable is in port 2 as suggested in the User Manual.

 

I can, however connect to the ComX510 using the WiFi dongle over 10.25.1.1, and see that the password requires changing (confirms factory reset worked).

 

The customer in a remote location is facing the same Ethernet connectivity issue on a factory reset ComX that displays a Green light. How might I assist him without sending a WiFi dongle?

 

1. Can't enter the IP address to the web browser.

2. Can't see the device on the network in File Explorer

3. Can't do either of the above when at another fixed IP on the same subnet. 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-09-03 05:54 AM

0 Likes
1
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-03 05:54 AM

Hi,

 

Please ensure that you have removed the power, held the buttons on the front of the Com'X down for at least 10 seconds while applying power.  Hold the buttons down until the LEDs begin to blink.

 

If you've followed this procedure and are still unable to communicate to the Com'X, please contact the Customer Care Center for your region for further assistance.

 

Thanks,

Randi

See Answer In Context

Reply
Replies 4
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-08-28 08:36 AM

0 Likes
3
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-28 08:36 AM

Hi,

 

Did you try to login and verify that the Com'X was factory reset?  The procedure for resetting the admin password is VERY similar to the procedure for factory resetting the Com'X. 

 

To factory reset, power from the Com'X must be removed.  Then, both buttons MUST be held down for at least 10 seconds (until the LEDs blink), while power is applied to the Com'X.

 

Once you log in, please verify the network settings are set to default.


Regards,

Randi

Reply
swil
Commander swil
Commander

Posted: ‎2019-09-01 05:47 PM

0 Likes
2
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-01 05:47 PM

Problem is after a factory reset I can't establish a connection over Ethernet. If I could see the change password prompt then the problem would be resolved.

 

I've seen ComXs that don't load with a green light (stay orange), and essentially they are broken.

 

In this case I've got a green light on a factory reset ComX and can't connect with an Ethernet port.

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-09-03 05:54 AM

0 Likes
1
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-03 05:54 AM

Hi,

 

Please ensure that you have removed the power, held the buttons on the front of the Com'X down for at least 10 seconds while applying power.  Hold the buttons down until the LEDs begin to blink.

 

If you've followed this procedure and are still unable to communicate to the Com'X, please contact the Customer Care Center for your region for further assistance.

 

Thanks,

Randi

Reply
swil
Commander swil
Commander

Posted: ‎2019-09-04 03:22 PM

0 Likes
0
680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-04 03:22 PM

Thanks a lot. I didn't read the user guide properly.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore