Link 150 with IEM 2055

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Link 150 with IEM 2055
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
dpellegrin_mans
Captain dpellegrin_mans
Captain

Posted: ‎2019-04-25 05:19 AM

0 Likes
3
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-25 05:19 AM

Link 150 with IEM 2055

Hi 

 

Getting difficulties to communicate with IEM 2055 devices with Link 150 via modbus RTU

 

All paramters modbus settings look ok.

 

Anyone did work with these 2 equipment?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-04-25 05:30 AM

1 Like
1
1136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-25 05:30 AM

Hi,

 

I'm not an expert on either of these devices.  However, I have a little experience with the iEM2055.  This device requires that each parameter (Voltage, Current, etc) be read as a separate read.  So, if you want to read Current you have to read only 2 registers @address 3000.  Even if there is contiguous data, the parameter needs to be read standalone (ex. Energy registers that are near each other.  You can only read 4 registers, not 8 to get both Energy readings).

 

I hope this helps.

 

Randi

Reply
Anonymous user
Not applicable

Posted: ‎2019-05-06 08:56 AM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-06 08:56 AM

IEM2055 will not respond correctly if the registers are not polled correctly.

Kindly ensure the below communication settings in serial port of Link 150 are the same with the settings in IEM2055 meter

1.Baudrate,Parity should be same in Link 150 and Meter

2.Connection details should be as below

Connection details between Link 150 and IEM2055 meter

1.Pin4 of Link 150 to be connected to 23 in IEM2055

2.Pin 5 of Link 150 to be connected to 24 in IEM2055

 

For IEM 2055 to test communication from web page you can use the slave ID of the meter and starting address as 31 with length of 20.This should give the response.

 

Termination resistor is optional. It is required in the case if there are too many devices connected on the same serial network or if the serial cable length is crossing 2000mts

Reply
Jun_Escano
Lieutenant JG Jun_Escano Lieutenant JG
Lieutenant JG

Posted: ‎2019-09-05 08:32 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-05 08:32 AM

this is indeed the way how you communicate with these meters. 

 

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore