Hello,
I have a project to integrate readings from a condensate meter (steam) into PME. Either the COM'X 210/510 are being considered to read the scaled pulse output from the device depending on whether on-board data logging is required.
Considering that the sensor/meter has an NPN scaled pulse output, it is important that the COM'X digital input card be of the same type.
What type are the COM'X 210/510 digital inputs? (E.g. NPN or PNP). Depending on the type of the COM'X digital inputs we may or may not require a PNP to NPN converter.
Thanks,
Hady
Link copied. Please paste this link to share this article on your social media post.
Hi,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Randi,
Thank you for your response. I will wire this setup on a test-bench and let you know.
Regards,
Hady