Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello,
I have a project to integrate readings from a condensate meter (steam) into PME. Either the COM'X 210/510 are being considered to read the scaled pulse output from the device depending on whether on-board data logging is required.
Considering that the sensor/meter has an NPN scaled pulse output, it is important that the COM'X digital input card be of the same type.
What type are the COM'X 210/510 digital inputs? (E.g. NPN or PNP). Depending on the type of the COM'X digital inputs we may or may not require a PNP to NPN converter.
Thanks,
Hady
Link copied. Please paste this link to share this article on your social media post.
Hi,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Randi,
Thank you for your response. I will wire this setup on a test-bench and let you know.
Regards,
Hady
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.