ComX not getting passed boot up screen

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX not getting passed boot up screen
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2020-02-07 06:54 AM

1 Like
12
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 06:54 AM

ComX not getting passed boot up screen

Does anyone have any fixes to get our ComX510 passed the boot up screen. We've done a power cycle and still no response. 

 

Any support greatly appreciated

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-26 08:29 AM

1 Like
0
2050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 08:29 AM

Hi,

 

This is an issue with Com'X firmware version 6.5.4.  However, this was resolved with Com'X firmware version 6.5.5, attached below.

 

We apologize for the inconvenience.

 

Randi

See Answer In Context

Attachments
Com'X 210 v6.5.5.zip
Com'X 510 v6.5.5.zip
Com'X 210 v6.5.5.zip
Com'X 510 v6.5.5.zip
Com'X 510 v6.5.5.zip
Reply
Replies 12
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-07 07:21 AM

0 Likes
11
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 07:21 AM

Hi,

 

What version firmware is the Com'X 510 using?

 

Thanks,

Randi

Reply
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2020-02-10 12:52 AM

0 Likes
10
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-10 12:52 AM

Hi Randi, we're on 6.5.4. 

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-10 04:07 AM

0 Likes
9
2087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-10 04:07 AM

Hi James,

 

Would you try changing the firmware version to 6.0.7 using the USB method?

 

Thanks,

Randi

Reply
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2020-02-10 05:26 AM

0 Likes
8
2081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-10 05:26 AM

Hi, downgraded to 6.0.7 and still on boot up screen. Any other ideas

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-10 06:13 AM

0 Likes
7
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-10 06:13 AM

Hi,

 

I don't have any other ideas other than to wait a bit.  Sometimes the Com'X takes a while to boot if there are a lot of devices configured.  Do you recall how many devices were configured on the Com'X?

 

Randi

Reply
Jun_Escano
Lieutenant JG Jun_Escano Lieutenant JG
Lieutenant JG

Posted: ‎2020-02-11 01:26 AM

0 Likes
6
2074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-11 01:26 AM

We are facing the same problem and tried to pass the boot screen for already few days. We have done a complete factory reset and then it was working. However when we uploaded the backup file we got the same problem..

I am going to test it with a 'new' COMX and see whether the backup file is giving the issue. 

Firmware 6.5.4

Capture.PNG

Reply
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2020-02-13 01:13 AM

2 Likes
1
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-13 01:13 AM

OK, we are now back and running and hopefully this could assist someone in a similar situation.

 

Also Note we did not have the back up configuration file either. Please don't ask why đŸ˜‰ 

 

 

Reverted the unit to 6.0.7. This allowed us to lift the Configuration file using the USB method.

USB Extraction Method 

 

Installed file on another ComX to validate. On opening the ComX Device Web pages found the file was corrupted.  Had to reassign gateways that were not linked to the Meters. Pretty straightforward.

 

Factory reset the original unit and then reinstalled the repaired configuration file. Took an age to reboot, about 1 hour but eventually got it working.

 

We're now back on FE.

 

Hope that helps someone in a similar situation. đŸ‘

Reply
Anonymous user
Not applicable

Posted: ‎2020-02-18 01:33 AM

0 Likes
0
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-18 01:33 AM

Hi @james-wood-tel,

 

Did you find your answer to the replies above?

If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.

 

But if you still in the same situation please do not hesitate to inform us here.

Reply
François_H
Lieutenant François_H Lieutenant
Lieutenant

Posted: ‎2020-02-26 08:00 AM

0 Likes
3
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 08:00 AM

@Jun_Escano 

Hello

 

Did you solved the issue ? I got the same issue firmware 6.5.4

 

Best regards 

 

François

 

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-26 08:29 AM

1 Like
0
2051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 08:29 AM

Hi,

 

This is an issue with Com'X firmware version 6.5.4.  However, this was resolved with Com'X firmware version 6.5.5, attached below.

 

We apologize for the inconvenience.

 

Randi

Attachments
Com'X 210 v6.5.5.zip
Com'X 510 v6.5.5.zip
Com'X 210 v6.5.5.zip
Com'X 510 v6.5.5.zip
Com'X 510 v6.5.5.zip
Reply
Jun_Escano
Lieutenant JG Jun_Escano Lieutenant JG
Lieutenant JG

Posted: ‎2020-02-26 08:54 AM

0 Likes
1
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 08:54 AM

After many resets and boots and backup logs it is working....but only once we've downgraded it to v6.0.7 which seems to be working as done by others before. 

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-02-26 08:55 AM

0 Likes
0
2044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 08:55 AM

The issue was introduced in 6.5.4.  Please upgrade to 6.5.5.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Š 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore