Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
116 | |
57 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
I have two Com'X210 (v6.5.4) installed within a single site. Each is connected to a different Modbus RTU network having custom models, both are measuring Current, Voltage (L-N) and Energy in real-time but only logging kWh at 30-minute intervals and both publishing data via FTP to a cloud site every hour.
Com'X #1 is connected to 12 no. Eastron SDM630 power meters
Com'X #2 is connected to 23 no. Carlo Gavazzi EM24-DIN power meters
The FTP transfer is working as intended but when the CSV file arrives in the cloud, the file is empty apart from the header (see attached)
Any ideas?
Link copied. Please paste this link to share this article on your social media post.
Hi Iain,
Here is the latest version of Com'X firmware, which addresses the issue you are having exporting data.
Please let me know if you have any questions or concerns.
Best regards,
Randi
Link copied. Please paste this link to share this article on your social media post.
Hi,
Would you send me the Custom Models you've created for these devices?
Thanks,
Randi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thanks Randi
I will give the new firmware version a try on my next install.
Iain
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.