Good Evening,
After upgrading the Com'X 510 that I am maintaining, I found the following bug that may trouble end users as they will not be able to trend anything with a negative value in the Historical Trending page or Real Time Trending page. Please find the following screenshot as proof of the issue at hand,
For the Historical Trending function,
For the Real Time Trending function,
As there are quite a lot of electronic loads (i.e. inverter fridge, inverter air-con, full house LED lighting with electronic control gear, etc.), my home load is net capacitive and is indicated as negative on the reactive power reading. This reading cannot be display properly in the trending graphical views.
Appreciate the development team look into correcting this behaviour in future firmware releases.
Best Regards,
Tan Kuan Khoon
Senior Specialist, Product & Application Engineering
Partner Projects & EcoBuildings Business
Schneider Electric Singapore.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks KK.
Yes..we noted this in our release notes under "known issues":
Negative measurements are not being displayed in the Real Time Trending graph, but are included in the Data Points table and export CSV [artf167752]
We will be correcting this issue in the next release, but I do not have the date yet.
James
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks KK.
Yes..we noted this in our release notes under "known issues":
Negative measurements are not being displayed in the Real Time Trending graph, but are included in the Data Points table and export CSV [artf167752]
We will be correcting this issue in the next release, but I do not have the date yet.
James