Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi Team,
In Australia and New Zealand, for NABERS application, we need to separately monitor Lighting, Power and HVAC circuits for energy consumption.
I am thinking of application of PowerTag in this scenario.
However I've been asked by few customers if its possible to use Com'X custom pages and show the values of all Lighting circuits as one total Energy value. (Sum of all PowerTag for lighting = Total Lighting Energy value). Same for Power and HVAC?
Has anyone played with Custom Web pages to create summation dashboard?
Link copied. Please paste this link to share this article on your social media post.
We have played created custom device drivers within the Com'X 510. We are pushing data from our gateway to Facilities Insights. This does work. On the Com'X 510 you will get some displayable data. Custom devices will not show on the Monitoring tab but will display in the Measurements tab. Here is an example.
If there is a tool or method for more custom pages we do not know about it.
Sincerely,
Michael
Link copied. Please paste this link to share this article on your social media post.
Thank you for mentioning PowerTag.
Link copied. Please paste this link to share this article on your social media post.
PowerTag looks like a non-USA product due to the size of the devices. Look like they are intended for IEC breakers rather than American style like QO or NF units.
Is this true?
Thanks,
Michael
Posted: 2017-06-23 10:50 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
The ComX510 custom web pages allows retrieval of topics through a web api. Once those values are returned, you are free to do whatever you would like to them (add them, multiply, etc) before displaying them on your page. I don't have any example page handy to show this, but I'd be happy to help you troubleshoot as you build your page.
Best Regards
Colton
Link copied. Please paste this link to share this article on your social media post.
How are you? I hope it's ok!
I am in a similar process integrating a Quaitrol ITM509 temperature recorder which communicates to COM X'510 via the Modbus RTU protocol. Could you share or indicate the steps or procedures you followed to customize the measurement table tab for devices that are not by default in the driver's own COM X'510?
I would greatly appreciate your support,
Thank you
Miguel Huaccha
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.