Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
113 | |
55 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Is it possible to Change PAS unit ID 255 to i.e. 247? The SCADA system do not allow slave ID higher than 247.
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Hello,
No, it is not possible to change the modbus ID 255 of the Panel Server.
However only a few number of information (such as the two 2 Digital inputs available on PAS600L or PAS800L) are reachable through this modbus ID.
All the measurements relative to downstream products (Modbus serial line products, modbus TCP/IP products, SE 802.15.4 wireless products) are reachable through their individual unit ID (with the possibility to change the value in the Panel Server web pages)
So perhaps, it is not really a problem for your architecture... to check
BR
Link copied. Please paste this link to share this article on your social media post.
Hello,
No, it is not possible to change the modbus ID 255 of the Panel Server.
However only a few number of information (such as the two 2 Digital inputs available on PAS600L or PAS800L) are reachable through this modbus ID.
All the measurements relative to downstream products (Modbus serial line products, modbus TCP/IP products, SE 802.15.4 wireless products) are reachable through their individual unit ID (with the possibility to change the value in the Panel Server web pages)
So perhaps, it is not really a problem for your architecture... to check
BR
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.