COMX'510 not work with Browser
Hi
We have been installed some COMX'510 gateway one of our renowned Pharmaceutical factory in Bangladesh which was running smoothly when installed. Now some devices is not connected with browser by IP we have got error message. I have trying latest version firmware with my personal pen drive it is not updated. what we will do to running the devices and how to connect with browser?
Note that one COMX'510 is still power LED orange not changes.
Regards
Samim
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
hello,
Have you waited for a long time (>30 minutes) to see if power led is going green ? Here the ComX is starting up, and if the ComX does not start it would mean that it is stuck. Do you have a back-up ? are you using it as local data logger /energy server ? As a modbus gateway ? Have you tried Factory reset ?
I see that ComX is not starting with 24VDC Power but only with PoE... Just power it and wait.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Samimul_Islam ,
On your video, Com'X510 has not finished start up. This is expected to have this kind of message.
For any issue between Com'X and Web browser, please check following topics:
- https://community.se.com/t5/Gateways-and-Energy-Servers/Log-into-Com-X-webserver/m-p/386609
- https://community.se.com/t5/Gateways-and-Energy-Servers/SSL-protocol-error-with-EBX510-with-google-C...
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi,
Please find the below information
Have you waited for a long time (>30 minutes) to see if power led is going green ?
Ans: we have waited long time more than 30 min but power LED is orange.
Do you have a back-up ?
Ans: No. Due to not enter in COMX510.
Are you using it as local data logger /energy server ?
Ans: Energy server
As a modbus gateway ? Have you tried Factory reset ?
Ans: No
I see that ComX is not starting with 24VDC Power but only with PoE... Just power it and wait.
Ans: I have connected PoE.
Note: we have trying to update firmware by personal pen drive it's not updated as per Schneider instruction. now what can I do?
BR
Samim
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi
Good day.
We can't access comx'510 with browser which we have seen error message as per attached file.
Can you please support in this regards to solve the issue?
BR
Samim
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello,
You are using 10.25.1.1 to connect to port 2 ?
If the Power led does not become green, it would mean that ComX510 is dead. Would suggest Factory reset.
If Power led is not green you can not perform upgrade with USB stick
Kind Regards
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi
We have did factory reset and COMX510 has default IP 10.25.1.1 to connect with port 2 and power LED is green. When I connect gateway with computer it show error message that means can't access the ComX510. Also try to update firmware by USB it not work. Please find the attached error message for your better understanding.
Can anyone to support how to solve the issue?
BR
Samim
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Samimul_Islam ,
Can you provide result of ipconfig /all when connected to COMX510 port 2 ?
Are you sure to have renamed the file on USB stick correctly as per User guide ?
Any firewall or endpoint protection on your laptop ?
If nothing works suggest to replace the COMX510 by PAS800.
Kind Regards
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Samimul_Islam ,
On your previous post, we can see 2 different errors for the same Com'X510.
Time out (pic 625):
SSL error (pic 626):
Time out error = Com'X does not answer. Com'X Web services can be reached (device fully started).
Possible reasons = Com'X not started, ETH configuration is not 10.25.1.1 (factory), product dead...
SSL error = Com'X embedded cipher suites are not compliant with the browser SSL requirements.
Check my post for similar issue.
In this case, only upgrade through USB port can solve your problem.
Please try to run a Modbus Function Code 43-14 on your device to read your current FW version.
Now your Com'X is factory reset, please try again to upgrade to v6.8.7 with USB key.
Com'X Energy Servers are no more supported. So I doubt tech support will help you on this topic.
As mentioned by Guillaume, last solution is to replace your Com'X510 by Panel Server PAS800.
Regards,
Solution Architect - France Operations