Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
I have gotten a COM'X 510 with 2.1.18 FW to send out emails through a configured SMTP. It is also configured to send a CSV report. When the emails come in, the message is empty, and there is no attached CSV report.
I have tried this with compression enabled and disabled.
I have made sure there is data 'in the buffer' to be sent.
Any ideas/suggestions?
Link copied. Please paste this link to share this article on your social media post.
Check to make sure the SD card inside the COM'X does not have the write lock switch engaged.
Posted: 2016-03-10 04:48 AM
Link copied. Please paste this link to share this article on your social media post.
Hi,
Please can you make sure that on the devices measurement table the topics are checked for logging and publication If only logging is checked, then the information will not be published.
Link copied. Please paste this link to share this article on your social media post.
Thanks for the reply Lazaro,
I can indeed confirm that both the logging and publishing check boxes are ticked for quantities that are showing values.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2016-04-20 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Hi, Steven
The publication is still in issue?
don't forget that Com'X only send unencrypted email.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Thanks Lazaro, it was determined that the write lock switch was engaged on the SD card. Thanks for the reminder about not using encryption!
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.