Hi All,
I saw there are two kinds of antennas for Panel Server, PASA-ANT1 & SMT10015, but not very sure of the difference.
https://www.se.com/ww/en/product/PASA-ANT1/ecostruxure-panel-server-antenna-ieee802-11-ieee802-15-4/
Is PASA-ANT1 only for the ZigBee signal and SMT10015 only for Wi-Fi signal?
Thanks
Link copied. Please paste this link to share this article on your social media post.
hello,
ANT1 is for PAS WiFi or Zigbee (802.15xxx)
SMT as stated is for LoRa (LPWAN) used in Prismaset active
PAS does not support LoRa today
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, you are right, the antenna PASA-ANT1 can be used for WI-Fi (connection to Wi-Fi plant) or IEEE802.15.4 communcation (to gather SE wireless product such as PowerTag)
Note that a guide ( https://www.se.com/ww/en/download/document/DOCA0289EN/) dedicated to Panel Server Wireless architecture delivers guidelines to obtain a reliable setup.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thanks for the information! One more thing to confirm, depending on where we install the ANT1 antenna, the function would be different, right?
I for Wi-Fi & N for Zigbee
Link copied. Please paste this link to share this article on your social media post.
Hello,
Yes, you are right, the antenna PASA-ANT1 can be used for WI-Fi (connection to Wi-Fi plant) or IEEE802.15.4 communcation (to gather SE wireless product such as PowerTag)
Note that a guide ( https://www.se.com/ww/en/download/document/DOCA0289EN/) dedicated to Panel Server Wireless architecture delivers guidelines to obtain a reliable setup.