Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
30 | |
28 |
Posted: 2022-05-09 06:33 PM . Last Modified: 2022-06-07 03:04 AM
Link copied. Please paste this link to share this article on your social media post.
Hi there,
Our customer gets a PR7 pulse water meter and we want to connect to Acti 9 SmartLink. Based on the user manual, the Ideal wiring : pulse cable should be connected to I1 or I2 and supplied with 24V, GND cable should be connected to 0V. This means a pulse will be generated when the voltage level from I1 or I2 drops from 24 V to 0V. This is a kind of "negative pulse " waveform.
Is there any expert who can shares their knowledge or experience if the SmartLink bar is accept this type of pulse? Thanks in advance.
Cheers,
Welly
Link copied. Please paste this link to share this article on your social media post.
Hi @welly_xu_quasar ,
Smartlink only accept pulse meters compliant with IEC 62053-31 (generally called the "S0-Pulse").
Saia Burgess made a good summary of the definition of the S0-Output.
https://sbc-support.com/uploads/tx_srcproducts/Applicationnote_S0puls_output_EN_V1.1_01.pdf
A pulse will be counted if:
According to the Honeywell documentation, it seems that the Yellow output is not compatible with Smartlink IO Channel. Can you check what is the difference with the Red output ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @welly_xu_quasar ,
It seems that the Smarlink IO Channel is counting during the up -> down edge of the pulse.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @welly_xu_quasar ,
Thanks for your question.
I've seen that you added a picture of schematics into the "cover photo" area.
Unfortunately, there, it is not very visible for the community members.
Would you be able to add your picture directly into the post (by replying) and using the "Insert Photos" button? 👇
This would be much helpful to bring you a relevant answer.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi @welly_xu_quasar ,
Smartlink only accept pulse meters compliant with IEC 62053-31 (generally called the "S0-Pulse").
Saia Burgess made a good summary of the definition of the S0-Output.
https://sbc-support.com/uploads/tx_srcproducts/Applicationnote_S0puls_output_EN_V1.1_01.pdf
A pulse will be counted if:
According to the Honeywell documentation, it seems that the Yellow output is not compatible with Smartlink IO Channel. Can you check what is the difference with the Red output ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @welly_xu_quasar ,
It seems that the Smarlink IO Channel is counting during the up -> down edge of the pulse.
Regards,
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.