Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Zigbee Maximum Distance Limits for PAS400/PAS600/PAS800

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Zigbee Maximum Distance Limits for PAS400/PAS600/PAS800
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Joshua_Luzon
Joshua_Luzon Cadet
Cadet

Posted: ‎2022-06-05 07:26 PM

1 Like
1
3877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-05 07:26 PM

Zigbee Maximum Distance Limits for PAS400/PAS600/PAS800

Firmware release notes for 1.2.0 and 1.3.1 provided the guidelines for Zigbee Green Power (IEEE 802.15.4) communication in terms of the limit for number of devices connected but not on the distance limitations. 

 

Can you provide the distance limits for ZGP for PAS series devices? Thanks 

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-06-06 01:02 AM . Last Modified: ‎2022-06-06 01:06 AM

4 Likes
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-06 01:02 AM

Hello Joshreginal,

 

  • For PAS400,PAS600,PAS800 in a metallic panel without External  antenna :

Prerequisite: Wireless Output Power is set on Low Level as mentioned in Panel Server User guide (refer to warning page 47 of Panel Server user guide )  

Radio Frequency propagation is a physical phenomenon. Therefore, it is identical between a PowerTag Link and an ESXP Panel Server and all the rules explained in the guide wireless PoerTag system guide DOCA0194EN can be applied.

Obviously, it means:

  • a maximum distance of 3 meters between the gateway and the wireless gateway
  • No full metallic partition between them
  • In case of switchboard with non-partitioned contiguous cubicles (example: Prisma/ Okken / Blokset ) : one gateway for 3 cubicles

 

  • For PAS800 with IEEE802.15.4 External antenna :

It will be possible to connect an external antenna (ref PASA-ANT1) to Panel Server Advanced PAS 800 (not possible with PAS400 / PAS 600 !) to extend the IEEE802.15.4 network outside the switchboard and communicate with devices such as ambient sensor (example: CL110) located outside.

In this case, it will be possible to set the wireless output power on "High" level for the external antenna.

This kind of architecture is very new and some information about wireless performance  will be available in doc NNZ58425 (not yet published) .

 

Best regards.

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Reply 1
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-06-06 01:02 AM . Last Modified: ‎2022-06-06 01:06 AM

4 Likes
0
3858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-06 01:02 AM

Hello Joshreginal,

 

  • For PAS400,PAS600,PAS800 in a metallic panel without External  antenna :

Prerequisite: Wireless Output Power is set on Low Level as mentioned in Panel Server User guide (refer to warning page 47 of Panel Server user guide )  

Radio Frequency propagation is a physical phenomenon. Therefore, it is identical between a PowerTag Link and an ESXP Panel Server and all the rules explained in the guide wireless PoerTag system guide DOCA0194EN can be applied.

Obviously, it means:

  • a maximum distance of 3 meters between the gateway and the wireless gateway
  • No full metallic partition between them
  • In case of switchboard with non-partitioned contiguous cubicles (example: Prisma/ Okken / Blokset ) : one gateway for 3 cubicles

 

  • For PAS800 with IEEE802.15.4 External antenna :

It will be possible to connect an external antenna (ref PASA-ANT1) to Panel Server Advanced PAS 800 (not possible with PAS400 / PAS 600 !) to extend the IEEE802.15.4 network outside the switchboard and communicate with devices such as ambient sensor (example: CL110) located outside.

In this case, it will be possible to set the wireless output power on "High" level for the external antenna.

This kind of architecture is very new and some information about wireless performance  will be available in doc NNZ58425 (not yet published) .

 

Best regards.

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore