Hello community,
Would jumping together the positives and negatives make the 4-wire configuration compatible with Panel Server 600 instead of the 2-wire, or would a converter be necessary?
Please, advise.
Link copied. Please paste this link to share this article on your social media post.
I recommend using a 2 to 4 wire converter to connect the PAS600 to a 4-wire daisy chain.