Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hello community,
Would jumping together the positives and negatives make the 4-wire configuration compatible with Panel Server 600 instead of the 2-wire, or would a converter be necessary?
Please, advise.
Link copied. Please paste this link to share this article on your social media post.
I recommend using a 2 to 4 wire converter to connect the PAS600 to a 4-wire daisy chain.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.