Dear expert,
We have this rack in DCO showed cooling redundancy n+7, this should not be right. What does it mean and how could we fix this?
Thanks ,
Ziqiang
(CID:118001832)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:53 PM . Last Modified: 2024-04-08 12:49 AM
Hi Ziqiang,
The cooling redundancy for a rack indicates the number of cooling units that can fail and still keep the airflow state of that rack OK. The following page contains the definitions: Cooling Redundancy
As far as I know, cooling redundancy is part of the 2D cooling calculations (and not a user defined parameter).
Kind regards
(CID:118001864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:53 PM . Last Modified: 2024-04-08 12:49 AM
Hi Ziqiang,
The cooling redundancy for a rack indicates the number of cooling units that can fail and still keep the airflow state of that rack OK. The following page contains the definitions: Cooling Redundancy
As far as I know, cooling redundancy is part of the 2D cooling calculations (and not a user defined parameter).
Kind regards
(CID:118001864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:53 PM . Last Modified: 2024-04-08 12:49 AM
Hi Jef,
Thank you. Is there any place I can check which cooling units could affect the rack?
Best Regards,
Ziqiang
(CID:118001907)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:53 PM . Last Modified: 2024-04-08 12:49 AM
Hi Ziqiang,
Right click on a rack, and select Simulate Impact, that should display a list of equipment (including the cooling units).
Kind regards
(CID:118001974)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:53 PM . Last Modified: 2023-10-22 09:38 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.