HI
How can i delete virtual sensors in Data Center Expert Version 7.2.0 ?
I can't delete that ... I can just remove from map but when i want add new devices it's not posible because virtual sensor tenure my lisense... please help me
Thanks
(CID:108827967)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:51 AM . Last Modified: 2024-04-08 04:22 AM
Hojjat,
Virtual sensors do not use licenses within StruxureWare Data Center Expert. It will add to the device count in the status bar in the lower right-hand corner of the client, but it will not use a node within your licensing.
To edit/delete virtual sensors (devices):
Regards,
Cory
(CID:108827970)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:51 AM . Last Modified: 2024-04-08 04:22 AM
Hojjat,
Virtual sensors do not use licenses within StruxureWare Data Center Expert. It will add to the device count in the status bar in the lower right-hand corner of the client, but it will not use a node within your licensing.
To edit/delete virtual sensors (devices):
Regards,
Cory
(CID:108827970)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:51 AM . Last Modified: 2023-10-22 09:38 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.