seems to be an error with the ddf for one of the selected devices

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • seems to be an error with the ddf for one of the selected devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
10
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

seems to be an error with the ddf for one of the selected devices

dco8.01  dce7.41  ups mode is  infraStruXure Symmetra 160k  

When I set up the PUE in the DCO need to use UPS data, the system prompts " There seems to be an error with the DDF for one of the selected devices. please consult DCIM support for an updated DDF"

(CID:110018342)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
8
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi Fred,

Currently reproducible - I have also tested this yesterday (by using DCE 7.4.2 and DCO 8.0.3), apparently some sensor parameter(s) not being reported correctly.  I believe this is going to be investigated asap, to figure out what specific information should be included in the "ddf" file and/or if there should be a need for an enhancement in a future version of DCE.

Kind regards

(CID:116364768)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Dear Jef Faridi,

Kindly share the DDF information(name along with version) if you have. Also please confirm if the device is Modbus or SNMP.

Thanks,

 Ragupathy Kandasamy.

(CID:116364772)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi All, 

I am also able to re-produce the following DDF error when I am trying to add the IT load script by selecting the UPS for creating Energy System. The UPS model is Symmetra 48 KW-PX 2 UPS. DCO version: 8.0.3

 

The UPS is discovered via SNMP. 

(CID:116364778)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hello DCIM community,

I faced the same issue using DCE v7.4.1 and DCO v8.0.4 for UPS devices:

-SY125K250DR-PDNB;

-SY16K48H-PD.

Both UPS devices got default DDFs.

Guys, how can I solve this error? Do I need to replace some DDFs? Which then are actual DDFs for mentioned UPS devices?

 

Thanks,

Janis Magazeinis

(CID:126165291)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi Janis,

To my knowledge this is expected to be fixed in a future version of DCE.

For the time being, as a sort of work around, maybe creating virtual sensor(s) (on DCE) and then using that in DCO could be tried out.

Kind regards

(CID:126165370)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Thank You for the answer, Jef! I have not tried yet, but hope that the upgrade or virtual sensors will solve the issue!

(CID:126171362)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi All,

  • I am facing the same error with UPS symmetra PX 250 / 500 in DCO 8.1 and DCE 7.4.3.
  • From my understanding the work around is to create Virual sensors till this is issue is being fixed in the next version ( I need to know this is supposed to be fixed in DCE or DCO or both of them? )

BR,

Sameeh 

 

(CID:126178882)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:05 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi Sameeh,

This is expected to be fixed in DCE.

Kind regards

(CID:126178945)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2024-04-08 02:40 AM

Hello,  it appears that DCE 7.5.0 may resolve this issue.  We would advise that users who are still running 7.4.3, or a prior version that is affected by this issue, please upgrade to 7.5.0 to confirm the problem no longer occurs.

If 7.5.0 does not resolve the issue please let me know.

 

Thanks.

(CID:129408844)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2023-10-22 09:36 PM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2023-10-22 09:36 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of