DDF. not same value.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DDF. not same value.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:03 AM . Last Modified: ‎2024-04-08 02:41 AM

0 Likes
8
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:03 AM . Last Modified: ‎2024-04-08 02:41 AM

DDF. not same value.

hello.

 

i have ddf file.

xxxx.xml

install dce.

but.

not same value.

 

snmp view from web page. temp is 24.4 C

but snmp view from dce.

temp is 244.0 C

why  *10 Value?

 

how fix it?

 

help me please.

 

thanks.

 

 

(CID:110017664)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

0 Likes
1
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

Dear Yongjin,

It looks to be scaling issue in the DDF. If you received the DDF file for your third party device from EcoStruxure IT Help Center-device support request, then please contact them again with DDF reference number so that they can modify the DDF to show you the correct scaling of the Temperature Sensor in DCE software.

Regards,

Bala

(CID:110017677)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

In response to DCIM_Support
0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

Thank you Bala

(CID:110018039)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:41 AM

Hi Yongjin Choi,

Structure of the DDF-file not so difficult: necessary corrections can be made independently. I can help with it.

(CID:110017754)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

Very thank you spezialist

I am using notepad. And i have an xml file.

Contents of xml file are below.

What should I fix ?

 

 


http://www.w3.org/2001/XMLSchema-instance" xsi:noNamespaceSchemaLocation="http://localhost/ddf_schema/apc_ddf_1_6.xsd" ddfid="FLSystem_FLS7100A" ddfname="FLSystem FLS7100A" ddfversion="1" canremove="yes">
1.6


FLSystem
FLS7100A
Cooling Device

humidity

_Setting Humidity



.1.3.6.1.4.1.22210.2.1.2.0

1



DDC400


temp

_Temperature



.1.3.6.1.4.1.22210.2.1.3.0

1



DDC400


humidity

_Humidity



.1.3.6.1.4.1.22210.2.1.4.0

1



DDC400


temp

_Cooling Error



.1.3.6.1.4.1.22210.2.1.5.0

1



DDC400


temp

_Heating Error



.1.3.6.1.4.1.22210.2.1.6.0

1



DDC400


humidity

_Humidity Error



.1.3.6.1.4.1.22210.2.1.7.0

1



DDC400


humidity

_deHumidity Error



.1.3.6.1.4.1.22210.2.1.8.0

1



DDC400


temp

_Setting High Temperature



.1.3.6.1.4.1.22210.2.1.44.0

1



DDC400


state
_Cooling Driving Status


.1.3.6.1.4.1.22210.2.1.9.0



stop_run_em
DDC400


state
_Heating Driving Status


.1.3.6.1.4.1.22210.2.1.10.0



stop_run_em
DDC400


state
_Humidity Driving Status


.1.3.6.1.4.1.22210.2.1.11.0



stop_run_em
DDC400


state
_deHumidity Driving Status


.1.3.6.1.4.1.22210.2.1.12.0



stop_run_em
DDC400


state
_Output Fan Status


.1.3.6.1.4.1.22210.2.1.14.0



stop_run_em
DDC400


state
_Output Comp1 Status


.1.3.6.1.4.1.22210.2.1.16.0



stop_run_em
DDC400


state
_Output Comp2 Status


.1.3.6.1.4.1.22210.2.1.18.0



stop_run_em
DDC400


state
_Output Heater1 Status


.1.3.6.1.4.1.22210.2.1.19.0



stop_run_em
DDC400


state
_Output Heater2 Status


.1.3.6.1.4.1.22210.2.1.20.0



stop_run_em
DDC400


state
_Output Heater3 Status


.1.3.6.1.4.1.22210.2.1.21.0



stop_run_em
DDC400


state
_Output Heater4 Status


.1.3.6.1.4.1.22210.2.1.22.0



stop_run_em
DDC400


state
_Output Heater5 Status


.1.3.6.1.4.1.22210.2.1.23.0



stop_run_em
DDC400


state
_Output Humiditifier1 Status


.1.3.6.1.4.1.22210.2.1.24.0



stop_run_em
DDC400


state
_Output Water Supply Status


.1.3.6.1.4.1.22210.2.1.25.0



stop_run_em
DDC400


state
_Output Water Drain Status


.1.3.6.1.4.1.22210.2.1.26.0



stop_run_em
DDC400


state
_deFan Driving Status


.1.3.6.1.4.1.22210.2.1.45.0



stop_run_em
DDC400


state
_Output Humiditifier2 Status


.1.3.6.1.4.1.22210.2.1.46.0



stop_run_em
DDC400


state
_Fire Fighting Status


.1.3.6.1.4.1.22210.2.1.47.0



stop_run_em
DDC400


state
_Cracoperation Status


.1.3.6.1.4.1.22210.2.1.48.0



run_stop_em
DDC400




0
0
1
1
*
0







2
0
1
1
*
0









.1.3.6.1.4.1.22210.2.1.13.0



Total Alarm Status Alarm Present
Total Alarm Status Alarm Cleared

warning
system

Total Alarm Status Alarm Present
Total Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.29.0



Over Current Alarm Status Alarm Present
Over Current Alarm Status Alarm Cleared

warning
system

Over Current Alarm Status Alarm Present
Over Current Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.30.0



High Temp Alarm Status Alarm Present
High Temp Alarm Status Alarm Cleared

warning
system

High Temp Alarm Status Alarm Present
High Temp Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.31.0



Water Supply Alarm Status Alarm Present
Water Supply Alarm Status Alarm Cleared

warning
system

Water Supply Alarm Status Alarm Present
Water Supply Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.32.0



Low Current Alarm Status Alarm Present
Low Current Alarm Status Alarm Cleared

warning
system

Low Current Alarm Status Alarm Present
Low Current Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.33.0



Comp1 Alarm Status Alarm Present
Comp1 Alarm Status Alarm Cleared

warning
system

Comp1 Alarm Status Alarm Present
Comp1 Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.34.0



Comp2 Alarm Status Alarm Present
Comp2 Alarm Status Alarm Cleared

warning
system

Comp2 Alarm Status Alarm Present
Comp2 Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.35.0



Heater Alarm Status Alarm Present
Heater Alarm Status Alarm Cleared

warning
system

Heater Alarm Status Alarm Present
Heater Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.36.0



Water Level Alarm Status Alarm Present
Water Level Alarm Status Alarm Cleared

warning
system

Water Level Alarm Status Alarm Present
Water Level Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.37.0



Humiditifier Alarm Status Alarm Present
Humiditifier Alarm Status Alarm Cleared

warning
system

Humiditifier Alarm Status Alarm Present
Humiditifier Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.38.0



Fan Alarm Status Alarm Present
Fan Alarm Status Alarm Cleared

warning
system

Fan Alarm Status Alarm Present
Fan Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.39.0



Leak Water Alarm Status Alarm Present
Leak Water Alarm Status Alarm Cleared

warning
system

Leak Water Alarm Status Alarm Present
Leak Water Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.40.0



Temp Sensor Alarm Status Alarm Present
Temp Sensor Alarm Status Alarm Cleared

warning
system

Temp Sensor Alarm Status Alarm Present
Temp Sensor Alarm Status Alarm Cleared





.1.3.6.1.4.1.22210.2.1.41.0



Humidy Sensor Alarm Status Alarm Present
Humidy Sensor Alarm Status Alarm Cleared

warning
system

Humidy Sensor Alarm Status Alarm Present
Humidy Sensor Alarm Status Alarm Cleared




(CID:110018038)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

Team-I would suggest not to edit the DDF files format based on my practical implementations at the site. Improper format of DDF may causes problems to the DCE performances in the future. I agree DDF format is simple, and easy to edit, but often we may not be able to verify on how the reference was taken. DDF team can surely help you in editing the DDF for you based on the issues that you report in continuous to your DDF reference number.

As far as I know, DDF team has got the right software tools to make changes and simulate the results as well. 

This way, you can also be sure that the DDF which you are using is the correct one. 

(CID:110018062)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
1
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi Yongjin Choi,

In above the specified DDF-file it is necessary to make corrections here (under .1😞

temp _Temperature .1.3.6.1.4.1.22210.2.1.3.0 .1 DDC400

The logic seems to me is clear and it isn't necessary to explain in detail. Or it is necessary?

 

It is supposed that you are a professional and you won't make silly mistakes about which warns Balaraman Jagadeesan.

 

Always I am glad to help practically.

(CID:110018139)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

In response to DCIM_Support
0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2024-04-08 02:40 AM

Sorry.

I work. Without internet.

thank you.

I fix it.

(CID:110019539)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2023-10-22 01:49 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:04 AM . Last Modified: ‎2023-10-22 01:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore