EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 10:45 PM . Last Modified: β2024-04-04 02:47 AM
Hello community,
Our customer has pdu's connected with Network Port Sharing. Some of them are stuck at Firmware Upgrade screen as you can see in the picture below. I solve some of them after resetting the PDU, however, some of them are still not upgrading their firmware.
SOme of the PDU's are stuck in blue screen as you can see in the picture below. I can't reset these PDU's.
What should I do? Do have to send these PDU to hardware service?Do I have any other option?
Thanks in advance,
(CID:134026446)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 10:45 PM . Last Modified: β2024-04-04 02:47 AM
Hello Erhan,
You can check this knowledge base article, lots of tips & tricks you can try:
http://www.apc.com/nl/en/faqs/index?page=content&id=FA293874
and this one contains more details about the network port sharing:
regards,
Cees
(CID:134026521)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 10:45 PM . Last Modified: β2024-04-04 02:47 AM
Hi, I would answer sooner, but I was unabled.
I had similar issues after firmware update with 2 PDU`s two months ago & nothing we did solved the problem. We had to replace both of the PDU`s.
We were unable to connect to the PDU through any known protocol, so our conlusion is that the firmware update didn`t pass. After last few times we decided not to update any more firmware`s on PDU devices unless we have replacments in stock & the client has a long down time period for DC.
(CID:134027632)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 10:45 PM . Last Modified: β2024-04-04 02:47 AM
Dear Erhan Yasar,
Tell us, please, did you solve your problem or not?
With respect.
(CID:134680070)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 10:45 PM . Last Modified: β2023-10-22 09:34 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.