netbotz snmp failed

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
4
410

netbotz snmp failed

This question was originally posted on DCIM Support by John Smith on 2019-05-09


I have an issue on a Netbotz 450. Every time I try and start the SNMP service it says:

 

SNMP Info Starting network management services: snmpd on port 161.

SNMP Failure Starting network management services: failed

 

I have tried updating to 4.6.2. Turning it on/off, rebooting it. Is there any other troubleshooting I can do?

(CID:143757068)

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
1
410

Re: netbotz snmp failed

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-05-09


Hi John,

It's not an issue I've really seen before. There may be some kind of corruption on the appliance. Make sure you're using a matching version of Advanced View with your Botzware. You may also want to consider upgrading them both to 4.6.4 which is the most recent.

If that doesn't resolve it, Back up the appliance. Next, reset the appliance to defaults:

http://www.apc.com/us/en/faqs/FA158175

 

Do not bring in the backup. Set up the IP and log in right away. Try turning on the SNMP daemon. does it still fail? If so, I suggest a tftp upgrade:

http://www.apc.com/us/en/faqs/FA176133

Do not use the "rootupgkeep" option in step 17.

Again, do not bring in the backup.

If this works, there was likely some corruption. You can try bringing in the backup at this point but if you do and the issue returns, there's something corrupt in the backup and you'll want to manually reconfigure.

 

Thanks,

Steve

(CID:143757073)

DCIM_Support
Picard
Picard
0 Likes
0
410

Re: netbotz snmp failed

This comment was originally posted on DCIM Support by John Smith on 2019-05-13


Thanks I will try this!

(CID:143757804)

DCIM_Support
Picard
Picard
0 Likes
0
410

Re: netbotz snmp failed

This answer was originally posted on DCIM Support by Justine Chester on 2019-05-10


Hi John,

 

Just to add on Steve's recommendation, the latest available firmware for Netbotz v3 (i.e. Netbotz 450) is v4.6.4. The latest Netbotz firmware can be downloaded from the link below:

 

https://www.apc.com/shop/uk/en/products/NetBotz-Firmware-v4-6-4-Rack-Monitor-570-451-Wall-Monitor-45...

 

Just in case the solution Steve did not do the trick, I strongly suggest updating the Netbotz appliance.

 

I hope this helps.

 

Regards,

 

Justine

(CID:143757133)

DCIM_Support
Picard
Picard
0 Likes
0
410

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.