Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:13 PM . Last Modified: 2024-04-03 02:43 AM
Hello,
I have a Circutor CVM-Mini power analyser setup on DCE but it's showing apparent power in watts only. I need to view it in kW.
The DDF I'm using is one of two Circutor DDF's available to download "Circutor CVM-NRG96-ITF".
The second DDF is "Circutor CVMK" and doesn't work with my CVM-Mini at all.
Can the "Circutor CVM-NRG96-ITF" DDF be altered to give kW readings?
The modbus memory map for the CVM-Mini is on page 23 of the PDF below
http://docs.circutor.com/docs/M98174001-03.pdf
Kind regards,
Brendan.
(CID:143756997)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:13 PM . Last Modified: 2024-04-03 02:43 AM
Hi Brendan,
Attached is a DDF with updated sensors that report in kW. I left the original sensors in watts in case you are currently monitoring this device in DCO as well. For proper DCO association power must be reported in watts, not kW. Let me know if you have any issues.
-Nick
(CID:143760524)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:13 PM . Last Modified: 2023-10-20 05:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.