netbotz 250 | temperature/humidity sensor dont appear on display.

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • netbotz 250 | temperature/humidity sensor dont appear on display.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

0 Likes
8
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

netbotz 250 | temperature/humidity sensor dont appear on display.

I instilled a series of netbotz 250 in several backstage APC, the problem is that in some of them the temperature/humidity sensor dont appear on display. what i can do do solve this issue?

(CID:126885531)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

0 Likes
6
2381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

Hi Helio,

What firmware is the 250 running?

What sensors exactly have you connected?

Do you have anything else connected?

Are you seeing any errors in the logs?

You state that some of them don’t show the sensors. Have you tried connecting the sensors that are detected to the devices that do not detect sensors?

What troubleshooting have you done?

 

Steve. 

(CID:126885572)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

0 Likes
6
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:36 AM

Hi Helio,

What firmware is the 250 running?

What sensors exactly have you connected?

Do you have anything else connected?

Are you seeing any errors in the logs?

You state that some of them don’t show the sensors. Have you tried connecting the sensors that are detected to the devices that do not detect sensors?

What troubleshooting have you done?

 

Steve. 

(CID:126885572)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

What firmware is the 250 running?

The latest NetBotz Rack Monitor 250 firmware.

 

What sensors exactly have you connected?

Temperature/humidity Sensor (AP9335TH).

 

Do you have anything else connected?

YES, Rack Access control handle Input and door contact Sensor (front and back door), network connection cable.

 

Are you seeing any errors in the logs?

No, only: No items to display.

 

You state that some of them don’t show the sensors. Have you tried connecting the sensors that are detected to the devices that do not detect sensors?

I did the following: In some of the rooms where the sensor does not appear, I replaced the rack manger 250 with a new one, and the new one appeared with no problems. so the problem is apparently not in the sensor but in the rack maneger 250. And I have many cases of these.

 

What troubleshooting have you done?

  1. Upgrade the firmware
  2. Plug and unplug the power cable.
  3. Connect some new sensor.  

 

 

Hélio

(CID:126886045)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

Hi Helio,

 

I suggest disconnecting all sensors and resetting the unit to defaults. Re-IP the unit and connect only one known good temp sensor. Don’t connect any alink terminators, etc. 

You also mentioned “the latest” firmware but I have seen where the latest is not always the easiest to find.. Please make sure you’re at version 6.5. 

Steve. 

(CID:126886043)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:10 AM . Last Modified: ‎2024-04-05 03:35 AM

I Steven,

i followed all the steps that you recomended, but a still have the same issue. ( temperature/humidity sensor dont appear on display).
I tryed to connect the sensor to other new netbootz and the sensor appear, so the problem is no on sensor, i have many netbootz (news from the box) with that issue.

do you have other recomendation for us??

 

 

result.txt

 

(CID:128059583)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

Hi Helio,

if the sensor works in another appliance and not on this one, it would seem to be specific to the appliance. If you disconnected everything else, reset the device, then connected only one sensor / cable, it would appear that the device has a failure and should likely be replaced. 

 

Steve. 

(CID:128059654)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

 Hello, Steve.

The problem is that I have many Netbotz with this problem, I already installed more than 60 new Netbotz 250 in this project and we have at least 20 with this problem.

Today I performed the following test:

1. Disconnect all sensors and restart the unit in defaults.

2. Upgraded the device to the new firmware 6.5

3. I connected only the good sensor

I've tried this on 6 devices with that issue, but I have the same result. (the temperature / humidity sensor does not appear on the display).

 

 

When i connect the sensor with a good Netbootz the result is positive (like i said the problem is not on sensor) :

 

 

Should i change all the netbotz with that problems?? ☹️ 

 

(CID:128060227)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

In response to DCIM_Support
0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2024-04-05 03:35 AM

Hi Helio,

 

Although it may take a little time to become visible, if it never does, there would seem to be an issue with the device. It does seem odd however that you'd have so many with issues. AP9335TH can be bad but if it shows up on one device (assuming no extensions), it should show up on all. I'd contact tech support and work through it with them and replace as necessary.


Steve

(CID:128060238)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2023-10-22 09:33 PM

0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:11 AM . Last Modified: ‎2023-10-22 09:33 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of