modbus/tcp

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • modbus/tcp
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

0 Likes
6
1721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

modbus/tcp

We have the DCE version 7.2.7 and we intend to manage a Stemac generator via Modbus / TCP, has already been made improtação the DDF file from DeepSea DSE 7420, however to complete the configuration for DCE received the communication error fault. They could help us.

(CID:105467799)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

0 Likes
1
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

Hi Jeremias,

 

The easiest way to troubleshoot communications issues between DCE and a modbus device is to start by going directly to the modbus gateway if one is being uses. For instance, the TSXETG100 gateway has the option to be able to poll the devices. If you take one or more of the registers from the DDF and try polling the device's slave address as entered in DCE from the gateway, does the gateway show the proper values? If it does not, the issue is between the gateway and the device. If you are getting values, continue troubleshooting farther out.

 

If you have a modbus over IP software (there are a few free or shareware utilities), try putting your computer on the same network segment as the DCE server. Now poll the gateway and slave address for the registers you used previously. If you do not receive data but you did when you went directly to the gateway for this test, the issue lies somewhere on the network. Maybe you would want to try on the same segment as the device. If that works and the segment DCE is on does not work, it is likely an issue with data being blocked by a firewall  / router.

 

Did you get the DDF from multivendorsupport@apc.com?

Does the model specified in the ddf match your Stemac generator model exactly?

What troubleshooting, if any, have you done?


Thanks,

Steve

 

 

(CID:105467805)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

0 Likes
1
1720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

Hi Jeremias,

 

The easiest way to troubleshoot communications issues between DCE and a modbus device is to start by going directly to the modbus gateway if one is being uses. For instance, the TSXETG100 gateway has the option to be able to poll the devices. If you take one or more of the registers from the DDF and try polling the device's slave address as entered in DCE from the gateway, does the gateway show the proper values? If it does not, the issue is between the gateway and the device. If you are getting values, continue troubleshooting farther out.

 

If you have a modbus over IP software (there are a few free or shareware utilities), try putting your computer on the same network segment as the DCE server. Now poll the gateway and slave address for the registers you used previously. If you do not receive data but you did when you went directly to the gateway for this test, the issue lies somewhere on the network. Maybe you would want to try on the same segment as the device. If that works and the segment DCE is on does not work, it is likely an issue with data being blocked by a firewall  / router.

 

Did you get the DDF from multivendorsupport@apc.com?

Does the model specified in the ddf match your Stemac generator model exactly?

What troubleshooting, if any, have you done?


Thanks,

Steve

 

 

(CID:105467805)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

In response to DCIM_Support
0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

Thanks Steve The DCE is directly connected to the DSE7420 lan private network, slave settings ID 10 and default ports. Using the same settings in the Deepsea DSE Configuration Suite works in network communication. It may be that the DDF file is incorrect. We will be requesting a new DDF file.

(CID:105468451)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

0 Likes
2
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

Hi Jeremias,

 

Im not familiar with that software but if it is using Modbus over ip, we should be able to do the same with StruxureWare.  If it is not using Modbus and is instead using another protocol, it's not really a valid test, it is just showing that it is on the network and not necessarily available via Modbus. What registers did you poll, can you send the DDF?

 

steve. 

(CID:105467825)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

In response to DCIM_Support
0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:42 AM . Last Modified: ‎2024-04-09 12:51 AM

Thanks Steve Yes uses Modbus over IP . Follow the DDF file

deepsea_generator_gencomm.zip

(CID:105467830)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:43 AM . Last Modified: ‎2024-04-09 12:50 AM

In response to DCIM_Support
0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:43 AM . Last Modified: ‎2024-04-09 12:50 AM

Thanks Jeremias, and the specific registers you were polling? Steve

(CID:105467831)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:43 AM . Last Modified: ‎2023-10-31 11:22 PM

0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:43 AM . Last Modified: ‎2023-10-31 11:22 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of