Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:46 AM . Last Modified: 2024-04-09 12:49 AM
Hi team,
Anyone have try to mapping KW sensor from PMM to rack PDU since their PDU was not metered but it was connected to APC PMM. However, after i created a virtual sensor for KW for each breaker and mapped into rack PDU, the measure KW dont show up in DCO.Any idea how to facing this issue. here same screen shot for the device association for virtual sensor to rack PDU and power capacity view from DCO.
The data center is a colo provider. All rack PDU are provided from their tenant.
(CID:105467864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:46 AM . Last Modified: 2024-04-09 12:49 AM
Hi Syaharuddin,
I think the best achievement could be via the Branch Circuit Monitoring feature in DCO - in a Branch Circuit Monitoring configuration, the system works as if you had power measurements at rack pdu level, only these measurements are really retrieved at PDP, RPP or PP level. Detail description available here: Configuring Branch Circuit Monitoring
Kind regards
(CID:105467892)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:46 AM . Last Modified: 2024-04-09 12:49 AM
Hi Syaharuddin,
I think the best achievement could be via the Branch Circuit Monitoring feature in DCO - in a Branch Circuit Monitoring configuration, the system works as if you had power measurements at rack pdu level, only these measurements are really retrieved at PDP, RPP or PP level. Detail description available here: Configuring Branch Circuit Monitoring
Kind regards
(CID:105467892)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:46 AM . Last Modified: 2023-10-31 11:06 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.