EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:12 PM . Last Modified: 2024-04-07 11:10 PM
Hi,
how can i get the celsius value in portal its showing in fahrenheit, i don´t find where can config this unit in POrtal
i use DCE portlet to show a temperature sensor, but it's show in fahrenheit and i need celsius
User display prefeence are spanish
(CID:123998781)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:12 PM . Last Modified: 2024-04-07 11:10 PM
Dear Miguel,
As far as I know, the unit which portal shows for the DCE sensor values are shown as per the region settings on the Server on which Struxureware Portal is installed. If possible, please verify the region setting and format of Server in which the Portal is installed in Control panel-region-format setting.
I also request you to make sure that you are able to view the values in Celsius on your DCE software as well.
Go to DCE server–Server Administration Settings–>Time settings->ensure "Server Locale" is set to the correct preference.
I also let other community experts to suggest on your query.
Regards,
Bala
(CID:123998806)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:12 PM . Last Modified: 2024-04-07 11:10 PM
Dear Miguel,
As far as I know, the unit which portal shows for the DCE sensor values are shown as per the region settings on the Server on which Struxureware Portal is installed. If possible, please verify the region setting and format of Server in which the Portal is installed in Control panel-region-format setting.
I also request you to make sure that you are able to view the values in Celsius on your DCE software as well.
Go to DCE server–Server Administration Settings–>Time settings->ensure "Server Locale" is set to the correct preference.
I also let other community experts to suggest on your query.
Regards,
Bala
(CID:123998806)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:12 PM . Last Modified: 2023-10-22 04:35 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.