connected APC PDUs UPS and inrows to DCE and got ddf error

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • connected APC PDUs UPS and inrows to DCE and got ddf error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:17 AM

0 Likes
8
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:17 AM

connected APC PDUs UPS and inrows to DCE and got ddf error

connected APC PDUs UPS and inrows to DCE and got ddf error. We scan connect to the devices and the sensor of the devices are available, but they remain on error

 

(CID:140215986)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:17 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:17 AM

Hi, what is the PN for PDU, UPS & Inrow?

Did you search for right ddfs on ddf site?

What is the error message?

(CID:140216011)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

UPS APC Smart-UPS SRT 8000VA RM 230

Inrow ACRD101

PDUs AP8958As

There were default ddf files for APC devices on DCE so we have not look for them. Is it required?

(CID:140216009)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

Hi Oscar,

 

If you're getting a DDF transfer error "Device status may be inaccurate due to attempt to transfer DDF failed", please check out k-base FA177004. It describes the reason for the error and how to resolve it.

Thanks,

Steve

(CID:140216013)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

Steven Marchetti sent link to check if you have FTP protocols blocked on SNMP cards.

I think this he is right regarding the issue.

Also it is good to update ddf files, no matter if it is APC equipment. 

Personally I couln`t get data from AP8858 without updating PDU ddf file.

 

(CID:140216020)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

Dear oscar dafauce,

Tell us, please, did you solve your problem or not?

With respect.

(CID:141269285)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:03 PM . Last Modified: ‎2024-04-03 04:16 AM

We got snmp walkfile and waiting for ddf to be developed for these systems

 

(CID:141269294)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:04 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:04 PM . Last Modified: ‎2024-04-03 04:16 AM

Ok, thanks for the good feedback 😀.

(CID:141269333)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 05:04 PM . Last Modified: ‎2023-10-22 04:27 AM

0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:04 PM . Last Modified: ‎2023-10-22 04:27 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.