VM DCE 7.3.1 - server errors

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • VM DCE 7.3.1 - server errors
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:42 AM . Last Modified: ‎2024-04-08 10:42 PM

0 Likes
5
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:42 AM . Last Modified: ‎2024-04-08 10:42 PM

VM DCE 7.3.1 - server errors

Hi All,

Recently, we have problems to log on to DCE server, and have to rebooted VM to solve the problems.

as the tool is very critical to us to monitoring our data centres.

I have a screenshot below, It was one of few issues in past few days. Could you suggest a solution please?

10/5/16 10:07:32.555 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.650 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.656 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.660 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.669 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.677 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:07:32.683 ERRR - Error handled: 500 null
(com.apc.isxc.common.integration.rest.RestExceptionResolver)
10/5/16 10:09:32.499 WARN - Session b500053e-8170-473a-b7f1-7d9de68bb662 was timed out
(com.apc.isxc.event.application.RestEventApplication)
10/5/16 10:09:32.503 INFO - Unregister event session: b500053e-8170-473a-b7f1-7d9de68bb662
10/5/16 11:35:19.836 INFO - Restarting software due to stop command from watchdog (triggered via local socket)
10/5/16 11:35:50.193 INFO - Restarting ISXC software
Thanks,
Minh

(CID:108827673)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

0 Likes
1
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

Hi Minh,

 

I'm not sure where you got these events from but they only appear to show API based errors and really nothing about the DCE server or any of the processes running (or not running) in it. Things like how often the issue occurs, when it started, what exactly the system has for resources, etc. are a few important things that you may want to look at when troubleshooting performance issues.

 

Again, these appears to be API based errors. Are you only having issues when attempting to connect via the API or is the web page and client also having issues? What version of DCE are you running? How many systems are monitoring DCE? Is it just DCO, do you have other 3rd party systems monitoring it? All these things need to be looked at and if you're not sure where to start, perhaps speaking with tech support directly may be your best bet to start troubleshooting this issue.

 

Steve

(CID:108827752)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

0 Likes
1
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

Hi Minh,

 

I'm not sure where you got these events from but they only appear to show API based errors and really nothing about the DCE server or any of the processes running (or not running) in it. Things like how often the issue occurs, when it started, what exactly the system has for resources, etc. are a few important things that you may want to look at when troubleshooting performance issues.

 

Again, these appears to be API based errors. Are you only having issues when attempting to connect via the API or is the web page and client also having issues? What version of DCE are you running? How many systems are monitoring DCE? Is it just DCO, do you have other 3rd party systems monitoring it? All these things need to be looked at and if you're not sure where to start, perhaps speaking with tech support directly may be your best bet to start troubleshooting this issue.

 

Steve

(CID:108827752)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

In response to DCIM_Support
0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

Thanks Steven, I'll further investigate and then contact local support for assistants. Minh

(CID:108827783)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

0 Likes
1
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

You might also double check how the resources/allocations are doing for your VM.   While not the same errors we ran into issues when our VM was running low on memory  DCE - Internal Error occured during "loading model...ActiveAlertMap" is the thread I had created when we started having issues.

 

(CID:108827755)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

In response to DCIM_Support
0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2024-04-08 10:42 PM

Hi Michael, Thanks for your respond. Currently, I'm running DCE -7.3.1 VM, could you help me out how to increase the memory, as StruxurewareCentral.ova is not allowed to edit any configurations Thanks, Minh

(CID:108827782)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2023-10-22 04:14 AM

0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:43 AM . Last Modified: ‎2023-10-22 04:14 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now