Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:56 AM . Last Modified: 2024-04-08 02:43 AM
Unable to find the versions of software between InfrastruXture Central 6.0.1 and StruxureWare Data Center Expert 7.x or the current revision. Anyone done this upgrade?
(CID:110015928)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:56 AM . Last Modified: 2024-04-08 02:43 AM
Rodney,
To upgrade to the most recent version, the upgrade path would be:
6.0.1 > 6.2 > 6.3 > 7.0.0 > 7.2.0 > 7.2.1 > 7.2.2 > 7.2.4 > 7.2.5 > 7.2.6 > 7.2.7 > 7.3.1 > 7.4.2
You can contact your local technical support for them to verify your software support and provide upgrades.
Regards,
Cory
(CID:110015932)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:56 AM . Last Modified: 2024-04-08 02:43 AM
Hi Rodney,
Yes, we have done the upgrade from 6.01 to 7.4.2(6.0.1 > 6.2 > 6.3 > 7.0.0 > 7.2.0 > 7.2.1 > 7.2.2 > 7.2.4 > 7.2.5 > 7.2.6 > 7.2.7 > 7.3.1 > 7.4.2). I know it is a lengthy process, but it is how it works.
Please do take the current full backup before proceeding for the upgrade. In case if there is any issue while upgrading, you can use the backup file for restoration.
Regards,
Bala
(CID:110015937)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:57 AM . Last Modified: 2024-04-08 02:43 AM
Hi Rodney Reddick,
Change, please, a post topic from DCO to DCE. The post interesting also has to be correctly identified.
Thanks.
(CID:110016365)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:57 AM . Last Modified: 2023-10-22 04:12 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.