Update Firmware AP7830 PDU
Attempting to update firmware on AP7830 PDU that is currently at version 1. Can the PDU be updated to v3.9.2 or does an earlier version need to be applied before jumping to v3.9.2. Also concerned if the PDU will drop power updating from v1 to v3 firmware.
(CID:132652837)
- Labels:
-
Data Center Expert
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:00 PM . Last Modified: 2024-04-04 11:22 PM
Hi Barry,
Good day!
This metered rack PDU uses an NMC1. If the firmware that it is running at is AOS v1.XX, you might need to upgrade it to at least v2.0.2 before upgrading it to the latest available version.
Upgrading the firmware directly to the latest version may cause the PDU losing web access or worse network access, which means a Hyperterminal may be needed to restore network access to it.
I hope this helps.
regards,
Justine
(CID:132653007)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:00 PM . Last Modified: 2024-04-04 11:22 PM
Hi Barry!
NMC firmware can be updated directly to the latest version.
PDU will not drop the load when you will update it's firmware.
(CID:132652985)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:00 PM . Last Modified: 2024-04-04 11:22 PM
Hi Barry,
Good day!
This metered rack PDU uses an NMC1. If the firmware that it is running at is AOS v1.XX, you might need to upgrade it to at least v2.0.2 before upgrading it to the latest available version.
Upgrading the firmware directly to the latest version may cause the PDU losing web access or worse network access, which means a Hyperterminal may be needed to restore network access to it.
I hope this helps.
regards,
Justine
(CID:132653007)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 07:00 PM . Last Modified: 2023-10-22 04:11 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.