Unable to discover snmp devices inDCE 7.2.1

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Unable to discover snmp devices inDCE 7.2.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

0 Likes
4
490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

Unable to discover snmp devices inDCE 7.2.1

DCE Version is 7.2.1

We are unable to discover the SNMP devices in DCE. Bellow are the trouble shoots done.

1. The UPS SNMP page was not getting opened in any browser.
2. We have trouble shooted and found FW issue with the same, and upgraded the FW to latest version 3.7.2
3. Again we are not able to discover both UPS in the DCE. Bellow are the trouble shooting done.
    1. UPS SNMP webpage is working well when connected directly to the SNMP card.
    2. When the UPS SNMP is connected to their network, the webpage is not opening in any computers connected in the LAN
    3. We have discussed with Network team and asked for any blocked ports for this devices. They said that in their LAN all the ports are open.
   4. The ping utility in the DCE pings both UPS ip without any loss.
   5. The ping is ok even on customer's computers which are connected in the network.
   6. Even they have checked the port status of UPS SNMP devices in thier CORE SWITCH and found all the ports are in open condition.

Kindly suggest if you have any solution on this.

(CID:97485144)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

0 Likes
0
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

Hi Navaneethan,

 

You state that when the NMC is connected directly (using crossover) you can access the web page but can not on the network. If this is from the same computer, this aspect of the issue is definitely a network issue. There could be issues with the versions of firmware and their browsers so make sure this test is done with the same computer. Still, the web page of the NMC may or may not work but that does not necessarily mean that the SNMP aspect of the card does not work. These use different protocols as does ping.

 

I would suggest using an SNMP polling software and while on the network (preferably on the same segment as the DCE server), see if you can poll any information from the card. If you can not, it is a network issue and it is up to the customer's network people to determine. We can not troubleshoot their network. 

 

You are also at an older version of DCE. 7.2.7 is the most recent and there could potentially be issues having to do with versions. You did not mention the UPS specifics though. Is this an APC UPS? Is it a 3rd party UPS? 

 

Lastly, we have a knowledge base document that outlines a number of troubleshooting steps for SNMP communications issues. K-base can be found here:

www.apc.com/site/support/index.cfm/faq/

Please search for k-base FA226273 -  How can I troubleshoot SNMP communications issues?

 

Steve

(CID:97485152)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

0 Likes
1
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:01 PM . Last Modified: ‎2024-04-09 11:38 PM

I know this is an old post however it might help someone in the future.

In the FA226273 I noted that it says 'you can only have on SNMP version enabled at a time'. Although I have found that not to be the case in most of my devices occasionally I find devices which see having both V1 and V3 enabled causes an issue.

Some older devices don't like having V3 enabled at all.

So try and disable V1 in the device and then run the scan.

I have two systems, one using V1 and one using V3 so this makes it difficult for me but at least a found a solution.

(CID:120133227)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:02 PM . Last Modified: ‎2024-04-09 11:36 PM

In response to DCIM_Support
0 Likes
0
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:02 PM . Last Modified: ‎2024-04-09 11:36 PM

John,

Just an FYI, the k-base says "Only 1 version should  be enabled on an APC device at a time." not "can only". We've also seen both enabled at the same time causing issues and that's why it was noted in the k-base since the app itself doesn't disallow it.


Steve

(CID:120133237)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:02 PM . Last Modified: ‎2023-10-31 11:39 PM

0 Likes
0
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:02 PM . Last Modified: ‎2023-10-31 11:39 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore