The server should not be supplied from different phases on 1 UPS

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • The server should not be supplied from different phases on 1 UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:57 AM . Last Modified: ‎2024-04-09 12:26 AM

0 Likes
2
577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:57 AM . Last Modified: ‎2024-04-09 12:26 AM

The server should not be supplied from different phases on 1 UPS

Hi all

I have been getting this recommendation from DCO 7.5.0 when a device with 6 power inlets is connected to phases L1, L2 & L3 on both AP8886 rPDU's or AP7557 rPDU's in the rack. I have noticed that the devices, typically HP C7000 blade chassis, are connected this way in the belief of balancing the load over each phase.

Q1. Is this a correct approach to balance phase load at the device level ?

Q2. If not then what is the reason for the recommendation ?

Q3. Would best practice be to connect the same phase on both rPDU's for the 6 power inlets ? (i.e. 6 x L1)

 

Thanks in advance

Jim Davis - NIE Melbourne. 

(CID:105470914)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:58 AM . Last Modified: ‎2024-04-09 12:26 AM

0 Likes
0
577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:58 AM . Last Modified: ‎2024-04-09 12:26 AM

Hi Jim

Normally the recommendation we give is to connect load on just one phase. I understand that there can be circumstances where you have to do something else.

There are a couple of reasons for this the advice to put load on a single phase:

  1. For some blade chassis it is difficult to know how much load is put on each of the power supplies, since sometimes a power supply powers only some blades or only the fans. If you have the power connections to different phases it is difficult (also for StruxtureWare Operation) to predict the load on each phase.
  2. If the load is connected to different phases in a setup with redundancy at the distribution level (all connections are at the top of the power path protected by the same UPS), then the UPS must reserve capacity for the full load of the blade chassis on both of the connected phases. Otherwise it cannot guarantee that the equipment can fail over to the other phase if there is a failure at the distribution level (for example if a PDU or rack PDU fails). This can in the worst case mean that you can only use half of the UPSs capacity. This is the reason for the recommendation you see in Operation.

If you can balance the load by putting one chassis on L1 and one on L2 and a third on L3 and so, I would recommend that instead.

I hope that helps.

Best,

Niels

(CID:105470925)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:58 AM . Last Modified: ‎2023-10-31 11:39 PM

0 Likes
0
577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:58 AM . Last Modified: ‎2023-10-31 11:39 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of