Hello All, I am new to using the TSXETG100 and have created a little test environment to convert from a Netbotz 200 RS485 Modbus serial output to the TSXETG100 and then using a tool called MODSCAN32 (but there are lots around) to view the Modbus registers.
The NB200 Modbus registers state that they range from 000h (0dec) to 0344h (834dec) but while I don't get any read errors (Modscan is saying it polling OK) I don't get any meaningful information from the TSXETG100.
I believe I am polling the NB200 correctly but I cannot interrogate any of the right registers (they all return 2 except for 40001 which returns 2.
Can someone point me in the right direction for a MODBUS/IP tool to read the registers in the appropriate range?
Thanks
Craig
(CID:96044736)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:21 PM . Last Modified: 2024-04-09 11:53 PM
Hi Craig!
In fact, you need to increase register number by 1 in order to obtain right information. So if you want to receive model name, for example, you need to start polling from register 40278 instead of 40277.
I think that your issue is related to results interpretation by Modscan software. I recomend you to try another one. I use CAS Modbus Scanner.
For find it out you can go to Diagnostic page of TSXETG and see what values are received by gateway.
For example:
(CID:96044772)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 12:22 PM . Last Modified: 2023-10-31 11:39 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of