Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:28 PM . Last Modified: 2024-04-05 12:33 AM
Hi,
customer has DCE and wants to see more than only the display firmware version like the main controller and power module firmware versions.
The only thing you see now is the Display firmware version.
See picture below
Is there a possobility to see the firmware of the main controller and the firmware of the power modules ?????.
and if not will this come in a newer version of the DCE visible ??.
Hope to hear from you soon.
(CID:129408689)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:28 PM . Last Modified: 2024-04-05 12:33 AM
Hi Frans,
From what I can see, these values are not available in the modbus register map for the Symmetra MW. If the device does not output the value, StruxureWare DCE can not provide that value in it's interface. To get DCE to show these values, you'd need to have those values in the device then have the DDF team include the values in the DDF. Your request would need to be made of the UPS engineering team, not DCE.
Thanks,
Steve
(CID:129408718)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:28 PM . Last Modified: 2024-04-05 12:33 AM
Hi Frans,
From what I can see, these values are not available in the modbus register map for the Symmetra MW. If the device does not output the value, StruxureWare DCE can not provide that value in it's interface. To get DCE to show these values, you'd need to have those values in the device then have the DDF team include the values in the DDF. Your request would need to be made of the UPS engineering team, not DCE.
Thanks,
Steve
(CID:129408718)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:28 PM . Last Modified: 2024-04-05 12:33 AM
Thanks Steve for your quick answer.
(CID:129412008)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:28 PM . Last Modified: 2024-04-05 12:33 AM
Sent off-line email
(CID:129408758)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:29 PM . Last Modified: 2023-10-22 04:04 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.