Switchgear genome can power but cannot have a breaker added?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Switchgear genome can power but cannot have a breaker added?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:35 AM

0 Likes
7
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:35 AM

Switchgear genome can power but cannot have a breaker added?

I have installed a generic switch gear to power my switchboard for my master breakers.  (switch gear is a red box, the switchboard the green boxes) Issue is, the switch gear can't have breakers added, and the switchboard requires breaker information under the power dependency tab.  How else do I show my switchboard as receiving power if I don't use the switchgear power output?

(CID:89063961)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi,

This looks fine. Switchgears are usually found in electrical rooms which are responsible to supply power at Infrastructure level & not at the rack level. For this reason, Isolators are deployed at Switchgears & not MCBs. Swtchgear usually deals with Busbar level coupling & decoupling & not associated with any breaking mechanisms, however sometimes they might be associated with Air Circuit Breakers. I think this design in DCO works well!

(CID:89063986)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:08 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Chris, Could you elaborate a bit on the used equipment and the power dependency/connections. It would be great to know the genomes used from the genome Library. I know the generic switch gear is used (which must be the red box named Switchgear in your setup?) What type of genome is used for the other component (LB-Master switch)? Also if possible talk a bit to the power connection going out of the room? Maybe a screenshot of the power dependency tab in DCO seen from the LB-Master switch point of view?

(CID:89063991)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Chris, Came to think if this is switch gear prior to your UPS(s)? In general DCO is currently not capable of understanding power connections going into the UPS. It can be modelled in terms of physical presence and to some extend connections. However please still see above comment regarding equipment used since I need to understand a little more in detail.

(CID:89063998)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

The genome used for the Master Switch, is the Generic Power Panel (GEN_PP). We have incoming utility power (switchgear), this feeds into our breakers (master switch) and this is where we divide into our UPS's and another breaker panel (in our data center using the same GEN_PP genome) that feeds our HVACs. By the way, Soren that power dependency is from the LB-Master PoV I was just trying to configure our rooms as accurately as possible. I see that the UPS's don't allow power input which is a little perplexing, but I can work around that and notate on my breakers. What I'd like though is show actual utility power feeding my breaker panel and being split from there. If this is the best I can do at the time, it is sufficient, just thought I'd shed some light on the issue for myself. I'm always up for learning how to better my DCO if possible though 🙂

(CID:89064007)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

Hi Chris,

As already discussed. In general DCO is currently not capable of understanding power connections going into the UPS and in general the power connections above the UPS level therefore also cannot be modelled. It can be modelled in terms of physical presence and to some extend connections however it will be limited as you experience.

In this case I would recommend using the generic power panel as you already have used and then add custom properties to document the connections.

(CID:89064030)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2024-04-10 01:34 AM

Thanks for elaborating and shedding some light. Please see the answer I have written.

(CID:89064031)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2023-10-31 11:37 PM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:09 AM . Last Modified: ‎2023-10-31 11:37 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of