StruxureOn GW: backup failed on \\localhost\C$ administrative shares?
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-0302:21 PM. Last Modified: ‎2024-04-0801:20 AM
StruxureOn GW: backup failed on \\localhost\C$ administrative shares?
Hi all!
Sometimes it is necessary to install and use the server software similar to StruxureOn Gateway, on Windows OS (7/8/10 or 2008/2012/2016) without registration in AD. It is normal both for test environments, and for productive.
But in that case it is possible to face above the specified problem: and it thus that the backup configuration in StruxureOn GW is absolutely true and checked (including access rights and passwords). At the same time in logfile C:\Program Files\StruxureOn Gateway\log\console.log we have mass here of such errors:
03/22/2017:21:38:17.341:ERROR:http-nio-443-exec-3 SmbFileSystem:190 - Change directory Exception: Access is denied.
SOLUTION:
If you are not in a AD: UAC will prevent remote access to administrative shares. Therefore it is necessary set registry option, which allows remote UAC: